Fishy smell from electrical panel??
#1
Member
Thread Starter
Join Date: Aug 2009
Location: USA
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts

So the past week my wife and I have smelled a fishy smell only when using our dryer. I thought maybe a rodent got in the vent or something and cleaned and inspected it and nothing in there, I walked past my panel and the smell was 100x worse so I popped it open only to smell that awful smell and know for sure it was coming from that. The breakers for my dryer were fairly hot to the touch, what does this mean and what can I do??


#2
Sounds like something is burning. That would suggest one of three problems.
1) The screw terminals on the side of the breaker are loose.
2) The breaker is internally defective.
3) The stab on the back of the breaker where it connects to the panel is loose/worn.
That should be addressed ASAP.
1) The screw terminals on the side of the breaker are loose.
2) The breaker is internally defective.
3) The stab on the back of the breaker where it connects to the panel is loose/worn.
That should be addressed ASAP.
#4
A service call from an electrician would run 100.00 - 125.00 here in NJ.
Probably less in your neck of the woods.
I can't make any recommendations because I don't know your comfort level around electric.
You could remove the panel cover and look without touching to see if anything is visibly burned. Do you have a friend or acquaintance that works with electric ?
Probably less in your neck of the woods.
I can't make any recommendations because I don't know your comfort level around electric.
You could remove the panel cover and look without touching to see if anything is visibly burned. Do you have a friend or acquaintance that works with electric ?
#5
Member
Thread Starter
Join Date: Aug 2009
Location: USA
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I used to work as an apprentice for commercial electrical construction for about 1.5 years so I have some experience and tools but that was over 10 years ago lol
I still remember some stuff and if you have any ideas of what I could do (hopefully diy) I'd love to try.
I'm very VERY careful with electrical and if I felt uncomfortable doing something I wouldn't do it for sure.
I still remember some stuff and if you have any ideas of what I could do (hopefully diy) I'd love to try.
I'm very VERY careful with electrical and if I felt uncomfortable doing something I wouldn't do it for sure.
#6
The first step is a visual check.
The second check is to TURN OFF the dryer breaker and check to see if the wire attaching screws are loose.
The third step is to unsnap the breaker out of the panel.
What brand is the panel ?
You could pop off the cover and shoot us a pic too. We can tell a lot of things from a picture.
The second check is to TURN OFF the dryer breaker and check to see if the wire attaching screws are loose.
The third step is to unsnap the breaker out of the panel.
What brand is the panel ?
You could pop off the cover and shoot us a pic too. We can tell a lot of things from a picture.
#9
Forum Topic Moderator
Nothing looks obviously bad. Breakers will get warm during normal operation, but they shouldn't be burn-your-fingers hot.
Do you notice the smell only when the dryer is running?
Do you notice the smell only when the dryer is running?
#10
Member
Thread Starter
Join Date: Aug 2009
Location: USA
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
It only smells when the dryer is going, but what's really weird is it's not necessarily every time the dryer goes, but most times.
When I went to put the panel cover back on I saw this and freaked out a little
When I went to put the panel cover back on I saw this and freaked out a little


#14
When I went to put the panel cover back on I saw this and freaked out a little


Originally Posted by Michael Rivers
Well, the location looks correct for it to be the dryer's breaker.
#15
The smoke on the back of the deadfront particularly seems to point that way. What is that breaker for, and have you inspected it
#16
i see major buss bar issues. The aluminum buss looks severely corroded. If the main is up then it's the right hand side connection from the main to the breakers.
Looks like your panel is taking on water from the service.
Looks like your panel is taking on water from the service.
#17
I have to agree , PJ. We don't know for sure if the panel has aluminum bus, it could be tin plated copper, but I suspect this is an older Bryant or Westinghouse panel with aluminum bus. The aluminum bus cannot withstand overheating.
#18
Member
Thread Starter
Join Date: Aug 2009
Location: USA
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I assume the buss bar(s) are what carry the current to the back of the breakers where they snap in?
I do see the corrosion but no trace of water in the panel. You guys think a house this old (about 40 years) should just be rewired and a new panel or what?
With as many problems as I'm finding I have a feeling that a lot needs to be done on my electric
I do see the corrosion but no trace of water in the panel. You guys think a house this old (about 40 years) should just be rewired and a new panel or what?
With as many problems as I'm finding I have a feeling that a lot needs to be done on my electric


#19
If you're panel is getting water in in it..... it usually comes from the service and in particularly the meter pan.
Take a look at your service where it comes into the electric meter. Is it the gray type cable ?
Where it enters the meter pan it's usually sealed with putty that may have dried out and cracked.
It's hard to make a recommendation to you without being there. When I get a call like that the first thing I'll do is open the meter. Unfortunately that is something that a homeowner should not do. I'll check for leaks and water. Water can follow the service cable right into the panel where it usually runs into the main breaker and runs down the buss bars to all the breakers.
You may need the services of an electrician there to at least survey the problem and make recommendations.
Take a look at your service where it comes into the electric meter. Is it the gray type cable ?
Where it enters the meter pan it's usually sealed with putty that may have dried out and cracked.
It's hard to make a recommendation to you without being there. When I get a call like that the first thing I'll do is open the meter. Unfortunately that is something that a homeowner should not do. I'll check for leaks and water. Water can follow the service cable right into the panel where it usually runs into the main breaker and runs down the buss bars to all the breakers.
You may need the services of an electrician there to at least survey the problem and make recommendations.
#20
Originally Posted by jbrdbr111
I assume the buss bar(s) are what carry the current to the back of the breakers where they snap in?
Originally Posted by jbrdbr111
You guys think a house this old (about 40 years) should just be rewired and a new panel or what?
#21
Member
Thread Starter
Join Date: Aug 2009
Location: USA
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Doesn't seem like anyone wants to work on panels, are they that bad? 3 electricians found excuses not to come out when I told them what kind if issue it is, guess I should just research how to do it myself?
#22
You guys think a house this old (about 40 years) should just be rewired and a new panel or what?
Originally Posted by Nick D.
Age is not really a factor in replacement. There is much electrical equipment 75 years and older that's still in regular service. If it's damaged to the point of not being repairable to good working order, then out it goes. (IMO)
#23
3 electricians found excuses not to come out when I told them what kind if issue it is, guess I should just research how to do it myself?