I need this explained : attic air handler needs 240v. I have double pole breaker reading 120 to ground each leg and 240 across. At other end of lines i also have 120 to ground each leg but only 78 volts between legs. Do i have a compromised line after breaker?
 
Sponsored Links
  #2  
Old 06-17-13, 09:14 AM
Member
Thread Starter
Join Date: Jun 2013
Posts: 2
There is no junction box between breaker and handler. Just lines from breaker go right to unit.
 
  #3  
Old 06-17-13, 09:18 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: NJ - USA
Posts: 43,494
Welcome to the forums.

If there is no splice point then it appears you have a defective piece of wire.

Possibly compromised with a nail or cut in some other way. Wire very rarely goes bad by itself.
 