Post-inspection question regarding grounding...

Had my electrical inspection and had this as part of the write up, "Use a listed splicing device (wire nut or other approved method) for all equipment grounds in all boxes." I'm used to taking the grounds and twisting them together, leaving a lead to secure to the receptacle or switch. Is he saying I need to take the ground wires, twist them in a cap, and run a lead from the cap to the switch or outlet?
 
Sponsored Links
  #2  
Old 06-27-13, 09:37 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,652
Received 517 Votes on 487 Posts
You can make a splice up like that or if you'd like to continue making up grounds like you've done in the past.... use a green wire nut. It has a hole in the center so that the nut part holds the splice together and one of the conductors will stick out of the wire nut and can go to the device.

Name:  green wire nut.JPG
Views: 1361
Size:  3.8 KB
 
  #3  
Old 06-27-13, 10:28 PM
Member
Thread Starter
Join Date: Jun 2013
Location: USA
Posts: 45
Received 0 Votes on 0 Posts
That looks perfect. I'll hit the store in the morning and pick up a bag. Thanks!
 
  #4  
Old 06-28-13, 05:34 AM
Member
Join Date: Jan 2012
Location: Canada
Posts: 2,739
Received 16 Votes on 15 Posts
That is pretty slick PJmax.
I've always used a standard wingnut and simply added a piece of scrap ground wire to the nut so I could mount it to the box (same general idea). The green one has the right colors and looks a bit cleaner.
Might see if these are easily available.
 
  #5  
Old 06-28-13, 06:23 AM
Member
Join Date: May 2013
Location: USA
Posts: 153
Received 0 Votes on 0 Posts
PJMax - That's slick. I love the look it provides. Do they make such an animal for the neutral and hot wire? Does code permit it other than the ground? Roger
 
  #6  
Old 06-28-13, 08:15 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
If I may answer for PJ, no, ground only because it works with bare wires. They are common as dirt. They have been around for many years and should be easy to find at building supply and hardware stores. However for neutral and hot you can use a wire nut with built in pigtail. They come with various colored pigtails.

(Updated image, thanks Vic.)
 

Last edited by ray2047; 06-28-13 at 10:11 AM.
  #7  
Old 06-28-13, 08:30 AM
Gunguy45's Avatar
Super Moderator
Join Date: Dec 2007
Location: USA
Posts: 21,119
Received 2 Votes on 2 Posts
Little better picture here Ideal Industries - Term-A-Nut Twist-on Pigtail Wire Connector

I'd use these if the grounds are already twisted and all cut to the same length.
 
  #8  
Old 06-28-13, 08:57 AM
Member
Join Date: May 2013
Location: USA
Posts: 153
Received 0 Votes on 0 Posts
What I like about the pigtails is one less conductor to twist together let say with 2 others. I'll have to keep my eyes open for them. Thanks. Roger
 
  #9  
Old 06-28-13, 12:04 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 8,470
Received 1 Vote on 1 Post
Or you could use a copper crimp collar and let one ground wire run long through it.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: