number of conductors in a box
#1
Member
Thread Starter
Join Date: Jun 2013
Location: usa
Posts: 3
Received 0 Votes
on
0 Posts
number of conductors in a box
I want to install 2 12-2 wires and a 20A outlet in a 4 x 2 1/8 x 2 1/8 metal box , bonded.
This is a total of 2 + 2 + 2 ( yoke) + 1 (ground) = 7 conductors . This is greater than NEC 314.16 code of 6.
This just does not seem practical. Many times you just want to go single box to box with just an outlet.
My question is do others violate this rule ?
Please do not respond just follow the NEC code.
Regards,
Robert
This is a total of 2 + 2 + 2 ( yoke) + 1 (ground) = 7 conductors . This is greater than NEC 314.16 code of 6.
This just does not seem practical. Many times you just want to go single box to box with just an outlet.
My question is do others violate this rule ?
Please do not respond just follow the NEC code.
Regards,
Robert
#3
Member
Thread Starter
Join Date: Jun 2013
Location: usa
Posts: 3
Received 0 Votes
on
0 Posts
thanks for the response wirenut110.
First I have a 4 x 2 x 2 box at 14.5 cuin.
next I took 7 conductors x 2.25 = 15.75 cuin.
15.75 is greater than 14.5.
Did I make a mistake in the calculations ?
First I have a 4 x 2 x 2 box at 14.5 cuin.
next I took 7 conductors x 2.25 = 15.75 cuin.
15.75 is greater than 14.5.
Did I make a mistake in the calculations ?
#5
Have to ask...whats a yoke? No electrician, but 12/2 would seem to only be 5 wires, since grounds only count as one. And I also read that wires that don't enter or leave the box (such as pigtails) aren't counted? Saw this exact same question on a search I did...and their calc was 18 (with internal clamps)...which would still be overfill of course.
#7
This is a total of 2 + 2 + 2 ( yoke) + 1 (ground) = 7 conductors. This is greater than NEC 314.16 code of 6.
next I took 7 conductors x 2.25 = 15.75 cuin.
next I took 7 conductors x 2.25 = 15.75 cuin.
Table 314.16(A) lists your 4 X 2-1/8 X 2-1/8 in. box as having a minimum volume of 14.5 in.[SUP]3[/SUP] and the maximum number of 12AWG conductors as 6.
Table 314.16(B) requires 2.25 in.[SUP]3[/SUP] of free space within the box for each 12AWG conductor.
In the text:
314.16 Number of Conductors in Outlet, Device, and
Junction Boxes, and Conduit Bodies. Boxes and conduit
bodies shall be of sufficient size to provide free space for
all enclosed conductors. In no case shall the volume of the
box, as calculated in 314.16(A), be less than the fill calculation
as calculated in 314.16(B).
(B) Box Fill Calculations. The volumes in paragraphs
314.16(B)(1) through (B)(5), as applicable, shall be added
together. No allowance shall be required for small fittings
such as locknuts and bushings.
(1) Conductor Fill. Each conductor that originates outside
the box and terminates or is spliced within the box shall be
counted once,
(4) Device or Equipment Fill. For each yoke or strap containing
one or more devices or equipment, a double volume
allowance in accordance with Table 314.16(B) shall be
made for each yoke or strap based on the largest conductor
connected to a device(s) or equipment supported by that
yoke or strap.
(5) Equipment Grounding Conductor Fill. Where one or
more equipment grounding conductors or equipment bonding
jumpers enter a box, a single volume allowance in accordance
with Table 314.16(B) shall be made based on the largest
equipment grounding conductor or equipment bonding jumper
present in the box.
With two 12-2/G cables and one receptacle, 1 for each conductor = 4, the equipment grounding conductors = 1, and a standard duplex receptacle = 2. That adds up to 7, which is 15.75 in.[SUP]3[/SUP].Junction Boxes, and Conduit Bodies. Boxes and conduit
bodies shall be of sufficient size to provide free space for
all enclosed conductors. In no case shall the volume of the
box, as calculated in 314.16(A), be less than the fill calculation
as calculated in 314.16(B).
(B) Box Fill Calculations. The volumes in paragraphs
314.16(B)(1) through (B)(5), as applicable, shall be added
together. No allowance shall be required for small fittings
such as locknuts and bushings.
(1) Conductor Fill. Each conductor that originates outside
the box and terminates or is spliced within the box shall be
counted once,
(4) Device or Equipment Fill. For each yoke or strap containing
one or more devices or equipment, a double volume
allowance in accordance with Table 314.16(B) shall be
made for each yoke or strap based on the largest conductor
connected to a device(s) or equipment supported by that
yoke or strap.
(5) Equipment Grounding Conductor Fill. Where one or
more equipment grounding conductors or equipment bonding
jumpers enter a box, a single volume allowance in accordance
with Table 314.16(B) shall be made based on the largest
equipment grounding conductor or equipment bonding jumper
present in the box.
That said, it doesn't seem reasonable that this box, which is the largest single-gang device box listed in Table 314.16(A), would be too small to allow the common practice of using two 12AWG cables to feed power in and out and supply one duplex receptacle. As you said,
This just does not seem practical. Many times you just want to go single box to box with just an outlet.
Maybe we're both missing something.
Last edited by pcboss; 06-30-13 at 08:58 PM.
#11
The ground wire has to be included in the first info box. The last info box only asks the size of the ground wire.

OK, that gives 15.8 in.[SUP]3[/SUP] needed and calls for a deep device box: 3 x 2 x 3.5"