Grounding a BX wire connection to new dishwasher

I am in the process of installing a new dishwasher however we seem to have BX cable running to the appliance. There is what appears to be a ground wire in the metal sheathing that has been cut very short but the previous owner did not have any ground wire going to the dishwasher box.

Do I need to trim the sheathing to expose a sufficient amount of ground wire? Alternately, I've read there is a clamp that can be used to connect BX wire to modern appliances with three wire connections. Or is there some alternate way to ensure that the dishwasher is safely grounded?

Thanks.
 
Sponsored Links
  #2  
Old 07-07-13, 09:08 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 13,057
Received 73 Votes on 65 Posts
No, With BX like you describe, the metal jacket is your ground. You can confirm this by taking a meter and checking between the hot wire and the metal jacket. You should get 120 volts. You need to use a proper connector for A/C cable (the NEC name of BX) The connection plate of the dishwasher should also be metal to carry the ground.
 
  #3  
Old 07-08-13, 01:46 PM
Member
Join Date: Aug 2009
Location: USA
Posts: 4,947
Received 0 Votes on 0 Posts
Make sure the ground wire from the dishwasher is connected to the metal box where you are connecting the BX. Use a proper cable clamp as Toylyn has already suggested, and make sure you have a red hat in there while you are at it.
 
  #4  
Old 07-08-13, 02:30 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,996
Received 39 Votes on 34 Posts
Type AC cable, commonly called BX, does not have a grounding conductor. If what you are describing is a thin uninsulated wire, commonly aluminum, it is the bond conductor. You don't need to do anything with it.
 
  #5  
Old 07-08-13, 03:16 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 8,470
Received 1 Vote on 1 Post
There is what appears to be a ground wire in the metal sheathing that has been cut very short but the previous owner did not have any ground wire going to the dishwasher box.

Do I need to trim the sheathing to expose a sufficient amount of ground wire?
If you have Type MC cable, which has a ground wire, then yes.

Both MC and AC are often referred to as BX. PCboss is right: the true descendant of BX is AC, which doesn't contain a grounding conductor.
 

Last edited by Nashkat1; 07-08-13 at 03:37 PM.
  #6  
Old 07-08-13, 08:02 PM
Member
Thread Starter
Join Date: Feb 2013
Location: USA
Posts: 5
Received 0 Votes on 0 Posts
What is the proper connector to secure the cable to the dishwasher? Videos I've seen described it just as a 'metal nut' that attaches the cable to the box but they didn't actually show how the connection worked.

Thanks for all the help.
 
  #7  
Old 07-08-13, 08:11 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
You use an armored cable connector. Example: https://www.foxelectricsupply.com/co...oductNo=ARL845
 
  #8  
Old 07-08-13, 08:35 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,996
Received 39 Votes on 34 Posts
Here are some AC and or MC connectors.

Flex • AC • MC Fittings
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: