GFCI Shutoff Breaker not testing
I just reinstalled the hot tub and shut off in a new location after we got a new patio poured. The shut off is fed by a 50 amp breaker in the main (sub) service panel. The wires between the service and the shut off are the same as I was using before and the wires between the spa and the shut off are new. All 6 awg THHN. After the install everything tested and powered up correctly (to the best of my knowledge anyway). When I tried the yellow "test" button on the GFCI in the shut off box, I heard buzzing and it seemed to only partially trip. I reset it and everything worked. I tried the "test" button again and now nothing happens. Everything worked and the GFCI "test" worked fine in the old location. Did the GFCI die? If so, any idea why? Here are some pictures of the wiring in the shut off...maybe I reconnected incorrectly?
#2
Here are some pictures of the wiring in the shut off...maybe I reconnected incorrectly?
Two thing I might try are 1> disconnecting the load wires and seeing if the GFCI will test and reset without the load, and 2> relocating the feed neutral to the lug at the top of the neutral bar. IDK why, it's just a "what if" guess.
On a side note, you need to replace the two "push penny" KO seals with weatherproof seals.
#5
Turns out it was a bad GFCI. Don't want to replace those very often ouch $$!
#7
I believe those Square D GFCI breakers have a lifetime warranty. You should be able to take it to a supply house that stocks Square D and get a new one for free.