I am making up a ten foot Liquid tight 3/4" conduit assembly. It will carry three #6 awg conductors for a 240 vac feed. I have a piece of #6 awg THHN white wire that is 40' long. Is it allowable to apply black and red electrical tape at the ends of the conductors to designate that there is a black, a red and a white conductor within the conduuit assembly?
Thanks
 

Last edited by pcboss; 07-28-13 at 06:05 AM. Reason: conduit was cable
  #2  
Old 07-25-13, 02:54 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 7,458
Upvotes: 0
Received 6 Upvotes on 5 Posts
I have a piece of #6 awg THHN white wire that is 40' long. Is it allowable to apply black and red electrical tape at the ends of the conductors to designate that there is a black, a red and a white conductor within the cable assembly?
No. Not only is it a white wire, it is too small. Only conductors larger than 6 AWG may be redesignated in the field.

Sorry 'bout that.
 
  #3  
Old 07-27-13, 04:39 PM
n1ml's Avatar
Member
Thread Starter
Join Date: Feb 2006
Location: South Florida
Posts: 447
Upvotes: 0
Received 2 Upvotes on 2 Posts
The good news is that I have one of the three wires that I need. Guess I need to get some black and red for the project.
Thanks
 
  #4  
Old 07-27-13, 05:36 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
You do not need a white for 240v. You can use two blacks.
 
  #5  
Old 07-27-13, 09:18 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 7,458
Upvotes: 0
Received 6 Upvotes on 5 Posts
Black, red and green, or 2 blacks and a green, or two reds and a green. An A/C condensing unit, if that's what you're supplying, does not require a neutral.

Save the white wire for another job.
 
  #6  
Old 07-28-13, 07:25 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,871
Received 185 Upvotes on 166 Posts
Black, red and green, or 2 blacks and a green, or two reds and a green. An A/C condensing unit
The green can be a #10, it doesn't need to be full sized.
 
  #7  
Old 07-29-13, 05:03 PM
n1ml's Avatar
Member
Thread Starter
Join Date: Feb 2006
Location: South Florida
Posts: 447
Upvotes: 0
Received 2 Upvotes on 2 Posts
Before I buy the wire,
I plan to use a red and a black #6 AWG and a green #10 AWG. Should I go with a #8 or #6 green or is that a dumb idea?
 
  #8  
Old 07-29-13, 06:13 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,976
Received 194 Upvotes on 170 Posts
Not a problem, just more expensive.
 
  #9  
Old 07-29-13, 06:15 PM
n1ml's Avatar
Member
Thread Starter
Join Date: Feb 2006
Location: South Florida
Posts: 447
Upvotes: 0
Received 2 Upvotes on 2 Posts
Thanks. I guess I will go with the #10 green.
 
  #10  
Old 07-29-13, 07:40 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 7,458
Upvotes: 0
Received 6 Upvotes on 5 Posts
Should I go with a #8 or #6 green or is that a dumb idea?
Not dumb, but more money than you need to spend.
I guess I will go with the #10 green.
Yep, good call.
 
 