New outlet from 3-way switch
Old 08-02-13, 07:20 AM
Hello. I am attempting to install new outlet for some low voltage lighting. The easiest place to do so is off of a 3-way switch. I was looking at 2 options and was hoping to get opinions.
It should be noted that I do have neutral wires tied together in the outlet box of the 3way switch.
Option 1 - Replace the existing 3-way switch with a combination 3-way switch/outlet. Only one outlet I know, but its at the end of the garage where I just do not see a need other than for the LV lighting.
Option 2 - Add an entirely new outlet next to the 3-way switch (tying into the neutral and hot from that 3-way switch.
Before I go down the path, I just wanted to make sure there are no flaws with these options.
As always, thanks for the assistance.
Todd
Old 08-02-13, 07:58 AM
Nashkat1's Avatar
So long as you have both a neutral and an unswitched hot available, either option should work. Because this is in your garage the receptacle needs to be GFCI protected. It might be easier to add a full-sized receptacle than to find a combination 3-way switch with a receptacle that is GFCI protected.
Old 08-02-13, 08:00 AM
ray2047's Avatar
Low voltage lighting transformers generally aren't rated for indoor use so I assume the receptacle will be outside. Finding a combo GFCI receptacle and 3-way switch might be difficult and certainly expensive. I'd say change to a double gang box and separate receptacle.
Old 08-02-13, 08:11 AM
Thank you both. I am assuming (hopefully correctly) that 2 of the wires going into the switch are the travelers and the remaining third is the unswitched hot. Could the 3rd be anything other than the unswitched hot?
Old 08-02-13, 10:01 AM
Nashkat1's Avatar
If you have one 3-conductor cable feeding that switch, and all three of the current-carrying conductors are connected to the switch, then you don't have a grounded conductor - a neutral - there.
Old 08-02-13, 10:04 AM
ray2047's Avatar
It could be switched power to the device controlled by the switch. There should be a 2-conductor cable in the box in addition to the 3-conductor. If disconnected it should show 120 volts when measured with a multimeter, solenoid tester, or test light. (A non contact tester can not be used.)