I was at my daughters house, when they pluged a light into a receptical. It sparked. I pulled the recp. out to see wiring charged and shorting out in box. fixed the wiring and replaced with new recp. No light. I'm getting 110v from ground wire to hot wire and 110v from ground to neut. But not across recp. from neut. to hot?
Old 08-12-13, 02:04 PM
Welcome to the forums.
You have an open neutral wire either at that location or before it gets there.
Old 08-12-13, 02:32 PM
why would I get 110 from ground to neut. on recp.?
Old 08-12-13, 03:07 PM
Somewhere on the circuit there is a device plugged in or connected. If the neutral gets lost that connected device will allow the hot to travel back up the neutral. The neutral completes the path to the panel......if it's open there is no completion of circuit.
Old 08-12-13, 04:04 PM
Nashkat1's Avatar
Have you tested that light in a different receptacle? Have you used a different light or other appliance to test this receptacle?
Old 08-12-13, 05:55 PM
recp.
yes. also there are other outlets out. guess have to trace it back.
Old 08-12-13, 06:20 PM
ray2047's Avatar
Remember to move any backstabs to the screws and the problem may be at either the last working or first non working receptacle. If any lights on the breaker the problem could be in a wire nut at a light or switch.