Overloading netural wire?
I have a 20Amp tandem breaker. They installed it using 12-3 romex wire. The black wire is on one circuit and the red wire is on the other circuit. Is it ok that these two wires share one neutral wire?
#2
Yes provided that the breaker is double wide and you measure 208-240 volts between the two breaker terminals where the red and black wires are connected respectively.
In other words you may not use the 3 conductor cable and share the neutral here if you measure 0 volts red to black (and 120 volts red to neutral and 120 volts black to neutral).
To meet the latest code the two breaker handles in question need to be linked together with an approved fastening so that if one trips, the other is flipped off.
In other words you may not use the 3 conductor cable and share the neutral here if you measure 0 volts red to black (and 120 volts red to neutral and 120 volts black to neutral).
To meet the latest code the two breaker handles in question need to be linked together with an approved fastening so that if one trips, the other is flipped off.
Last edited by AllanJ; 09-09-13 at 04:23 PM.
#4
Member
Thread Starter
Join Date: May 2013
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The breaker isn't a double wide. It only takes up one slot. I'm not currently at my house, but Ill have to check it out. I currently have 3 tandem breakers two 15AMP and one 20AMP breaker. They are all hooked up with 12-3 wire so I was just wondering if this was a problem or not.
#5
This one is a long shot because you might not find one that fits your panel.
You could use a quad tandem breaker that is double wide, using breakers 1 and 4 for one of the 3 conductor cables and using breakers 2 and 3 for another 3 conductor cable. There would need to be provison for handle ties that connect the respective handle combinations.
You could use a quad tandem breaker that is double wide, using breakers 1 and 4 for one of the 3 conductor cables and using breakers 2 and 3 for another 3 conductor cable. There would need to be provison for handle ties that connect the respective handle combinations.
#6
The breaker isn't a double wide. It only takes up one slot. I'm not currently at my house, but Ill have to check it out. I currently have 3 tandem breakers two 15AMP and one 20AMP breaker. They are all hooked up with 12-3 wire so I was just wondering if this was a problem or not.
#7
If this is a GE panel a twin will work if it is placed right but this is a tandem in most other panels as stated it is unsafe. Ask the people who did the work to come back and correct it on their dime.
#8
Member
Thread Starter
Join Date: May 2013
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The model # of the panel is BR2040BC200. Unfortunately I would contact the people that built the house, but they went bankrupt.
Is there a reason why they decided to use 12-3 wiring for this type of circuit? I have explained my situation to a Lowes employee and he said it wasn't a big deal. The only reason it caught my eye was a ran a new circuit in the basement for a treadmill.
So what is the proper way to wire a single wire tandem breaker? I ask this because I want the fridge and the over the range microwave on there own 20AMP dedicated circuit.
Since I have 3 tandem breakers installed incorrectly with 12-3 wire would it be ok to tie in the two 15AMP tandem breakers to the quad breaker? Then the remaining 20AMP tandem breaker can be replaced with a double pole breaker?
Is there a reason why they decided to use 12-3 wiring for this type of circuit? I have explained my situation to a Lowes employee and he said it wasn't a big deal. The only reason it caught my eye was a ran a new circuit in the basement for a treadmill.
So what is the proper way to wire a single wire tandem breaker? I ask this because I want the fridge and the over the range microwave on there own 20AMP dedicated circuit.
Since I have 3 tandem breakers installed incorrectly with 12-3 wire would it be ok to tie in the two 15AMP tandem breakers to the quad breaker? Then the remaining 20AMP tandem breaker can be replaced with a double pole breaker?
#9
Sounds like,e it may be time for a sub panel to make room for the new circuits and straighten the other one out.
#10
The model # of the panel is BR2040BC200
Is there a reason why they decided to use 12-3 wiring for this type of circuit?
I have explained my situation to a Lowes employee and he said it wasn't a big deal.
So what is the proper way to wire a single wire tandem breaker? I ask this because I want the fridge and the over the range microwave on there own 20AMP dedicated circuit.
Shop Eaton Type BR 20-Amp Quad Circuit Breaker at Lowes.com
Some electricians and builders use the 20-40 panel for savings, but my opinion is that the added cost of tandem and quad breakers washes out any savings and just creates a cramped panel.
#11
I have a 20Amp tandem breaker. They installed it using 12-3 romex wire. The black wire is on one circuit and the red wire is on the other circuit. Is it ok that these two wires share one neutral wire?
Two 120V circuits that share a neutral are known as a multiwire branch circuit. It must be wired so that the two hot wires are fed by the two different legs of your single-phase 120/240V service. That's not possible with a side-by-side handle pair, and is tricky to do properly with two half-high breakers.
So what is the proper way to wire a single wire tandem breaker?
I ask this because I want the fridge and the over the range microwave on there own 20AMP dedicated circuit.
To meet the latest code the two breaker handles in question need to be linked together with an approved fastening so that if one trips, the other is flipped off.
#12
Member
Thread Starter
Join Date: May 2013
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Here is a picture for a better understanding of what Im talking about.
Here is a run down of what items are on these tandem circuits.
20A
-master bath and guest bath(GFCI)
-3 outlets around stove(GFCI)
15A
-Fridge (draws 8.5A)
- GD (4A), Dishwasher (8.1A)
The other 15A tandem just powers on a few lights and bath room exhaust fans. I'm more worried about the breaker with the fridge, GD and Dishwasher. My plan was to remove the circuit from the fridge so the GD and the dishwasher would be on there own circuits.
Would it be ok to buy a 15A quad breaker to tie in the two 15A tandem breakers?
Here is a run down of what items are on these tandem circuits.
20A
-master bath and guest bath(GFCI)
-3 outlets around stove(GFCI)
15A
-Fridge (draws 8.5A)
- GD (4A), Dishwasher (8.1A)
The other 15A tandem just powers on a few lights and bath room exhaust fans. I'm more worried about the breaker with the fridge, GD and Dishwasher. My plan was to remove the circuit from the fridge so the GD and the dishwasher would be on there own circuits.
Would it be ok to buy a 15A quad breaker to tie in the two 15A tandem breakers?
Last edited by word2yamutha; 09-12-13 at 01:25 PM.
#13
Would it be ok to buy a 15A quad breaker to tie in the two 15A tandem breakers?
OK, couldn't find a picture, but the catalog number would be BQ215220. The center two poles are 20A with a handle tie and the outer two poles are 15A with a handle tie. Finally found a picture, check this out. This will replace the 20 amp tandem and the 15 amp tandem breakers in the picture.
https://www.platt.com/platt-electric...px?zpid=652295
Last edited by CasualJoe; 09-12-13 at 02:06 PM.
#15
Member
Here is a picture for a better understanding of what I'm talking about.
There seems to be one extra wire in there, or is it just the angle of the photograph?
Thank you,
#17
Its not the greatest picture, but there is another 15A tandem breaker below it.
#18
Member
Thread Starter
Join Date: May 2013
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
When you mix different Amp breakers on a quad breaker does it reduce the load? For example, if I tied in a 20A and a 15A in a quad breaker?
Im just trying to save space in my panel as I only have one slot left. Basement will be finished eventually. Id rather not install a sub-panel if possible.
Also, where is a good place to find cheap 12-2 NM romex cable?
Ok just want to make sure I get the correct breaker. I can use this to tie in the two 15A tandem breakers I have, correct?
Eaton 15 Amp 2 Poles BR Type Breaker, BQC Quad Breaker-BQC215215 at The Home Depot
Im just trying to save space in my panel as I only have one slot left. Basement will be finished eventually. Id rather not install a sub-panel if possible.
Also, where is a good place to find cheap 12-2 NM romex cable?
Ok just want to make sure I get the correct breaker. I can use this to tie in the two 15A tandem breakers I have, correct?
Eaton 15 Amp 2 Poles BR Type Breaker, BQC Quad Breaker-BQC215215 at The Home Depot
#19
When you mix different Amp breakers on a quad breaker does it reduce the load? For example, if I tied in a 20A and a 15A in a quad breaker?
Also, where is a good place to find cheap 12-2 NM romex cable?
Ok just want to make sure I get the correct breaker. I can use this to tie in the two 15A tandem breakers I have, correct?