Sub panel question.
#1
Member
Thread Starter
Join Date: Sep 2013
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Sub panel question.
I have a wire connecting my sub panel to my main 200 amp service. this is what it says:
Conal co-s type se cable style u type XHHW CDRS 300v to ground CDRS 4 AL 1 CDR 6 AL (UL)
It currently has a 50 amp breaker feeding it on a run of 30 ft. My question is what is the largest breaker that I can feed this sub panel with? Can I go with a 60 amp or even 100amp?
Other info:
Im putting in a new kitchen and Needed a few spaces for GFI's, and a microwave. The sub panel currently feeds my workshop and woodworking equipment. I dont think it would ever be above 70 amps per say unless I was using vacuum, saws and the wife had her mixer and a few other things running at the same time.
TIA!
Conal co-s type se cable style u type XHHW CDRS 300v to ground CDRS 4 AL 1 CDR 6 AL (UL)
It currently has a 50 amp breaker feeding it on a run of 30 ft. My question is what is the largest breaker that I can feed this sub panel with? Can I go with a 60 amp or even 100amp?
Other info:
Im putting in a new kitchen and Needed a few spaces for GFI's, and a microwave. The sub panel currently feeds my workshop and woodworking equipment. I dont think it would ever be above 70 amps per say unless I was using vacuum, saws and the wife had her mixer and a few other things running at the same time.
TIA!
#2
Do you have two or three insulated conductors in that cable? If you have only two, it will need to be replaced if it is in the same building as your service.
#4
it only has 2 insulated wires and one non insulated ground
My question is what is the largest breaker that I can feed this sub panel with? Can I go with a 60 amp or even 100amp?
The important consideration, though, is not what would it take to max out your existing subpanel. What's important is what the load on that panel will be.
Do a residential load calculation to determine the size of the conductors and the breaker. If you have Excel, you can use the calculator template available here: Mike Holt Free Resources Menu.
Last edited by Nashkat1; 09-15-13 at 07:31 AM.
#5
type se cable style u type XHHW CDRS 300v to ground