Physcal location of Main LC in relation to the service enterance.
#1
Member
Thread Starter
Join Date: Sep 2013
Location: USA
Posts: 74
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Physcal location of Main LC in relation to the service enterance.
It looks like our new build is going to be a go!
Now comes the final planning stuff so I can get my permit pulled and our utility provider to start trenching.
I have looked through the NEC and searched this forum (and others) regarding the location of my main load center in the house. The only logical place to up the meter is on the NE corner of the house due to the nature of our lot. This wall is a family room wall, and I am not too excited about having the LC in the room for aesthetic reasons. What is the official word on how far a panel can be located from the service entrance? I have found wording saying a "reasonable distance", but is there a max distance? How would I get around putting the panel in the family room? Is a CPVC pipe run through the ceiling to the utility room a possibility? Could it be run under the concrete floor?

I have looked through the NEC and searched this forum (and others) regarding the location of my main load center in the house. The only logical place to up the meter is on the NE corner of the house due to the nature of our lot. This wall is a family room wall, and I am not too excited about having the LC in the room for aesthetic reasons. What is the official word on how far a panel can be located from the service entrance? I have found wording saying a "reasonable distance", but is there a max distance? How would I get around putting the panel in the family room? Is a CPVC pipe run through the ceiling to the utility room a possibility? Could it be run under the concrete floor?
#2
The power company will determine where the drop or lateral should go. Where I live the main panel is almost always outside directly under the meter socket.
Usually six feet or less for a unfused line however you can put a main disconnect at the meter or use a meter socket that is combined with a main disconnect and there is no limit on distance.
What is the official word on how far a panel can be located from the service entrance?
#3
Member
Join Date: Dec 2003
Location: USA
Posts: 929
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Usually six feet or less for a unfused line however you can put a main disconnect at the meter or use a meter socket that is combined with a main disconnect and there is no limit on distance.
#4
Usually six feet or less for a unfused line however you can put a main disconnect at the meter or use a meter socket that is combined with a main disconnect and there is no limit on distance.
Is a CPVC pipe run through the ceiling to the utility room a possibility?
Could it be run under the concrete floor?
#6
I just talked to my inspector... He said the LC has to be directly behind the meter. Humf.
#8
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 1,983
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The "Main" circuit-breaker (MCB) that connects to the "Load" terminals of the Meter-Socket serves two purposes- (1), it's the Service Disconnecting Means and (2) , it's the Over-current Protective Device for the Conductors that terminate on the MCB "Load" terminals.
The Conductors that terminate on the "LIne" terminals of the MCB are "Service Conductors" ; the Conductors that terminate on the "Load" terminals are "Feeder Conductors" which are Conductors between the Service Equiptment and the individual "Branch-Circuits" of a "Load Center"
There is no limit on the distance that the Feeder Conductors can extend from the Service Equiptment to their termination-point on a Load Center in a Code-approved location.
A Code-approved "Wiring Method" is necesary for routing the Feeder Conductors between the two termination-points , and the constuction of the building often determines which WM is best.
I once installed Feeders in a multi Dwelling-Unit structure for a builder who "wanted the best", so the we used 2" Rigid Steel Conduit as the WM for each of the Feeders with the Conduit implaced in the basement floor concrete slab.
The Conductors that terminate on the "LIne" terminals of the MCB are "Service Conductors" ; the Conductors that terminate on the "Load" terminals are "Feeder Conductors" which are Conductors between the Service Equiptment and the individual "Branch-Circuits" of a "Load Center"
There is no limit on the distance that the Feeder Conductors can extend from the Service Equiptment to their termination-point on a Load Center in a Code-approved location.
A Code-approved "Wiring Method" is necesary for routing the Feeder Conductors between the two termination-points , and the constuction of the building often determines which WM is best.
I once installed Feeders in a multi Dwelling-Unit structure for a builder who "wanted the best", so the we used 2" Rigid Steel Conduit as the WM for each of the Feeders with the Conduit implaced in the basement floor concrete slab.
#9
There is no limit on the distance that the Feeder Conductors can extend from the Service Equiptment to their termination-point on a Load Center in a Code-approved location.
scubawes
I just talked to my inspector... He said the LC has to be directly behind the meter. Humf
I just talked to my inspector... He said the LC has to be directly behind the meter. Humf
#11
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 1,983
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Is the inspector's placing a "restriction" an arbitrary decision, or is he citing an NEC violation? ; if his citation is indeed based on the NEC , what is relevant Code Article?.
The crux of this issue is the obvious distinction between "Service Conductors" and "Feeder Conductors" , and both are well-defined in the NEC.
Just Curious; "scubawes" , where did you finds the words "reasonable distance"?.
The crux of this issue is the obvious distinction between "Service Conductors" and "Feeder Conductors" , and both are well-defined in the NEC.
Just Curious; "scubawes" , where did you finds the words "reasonable distance"?.