Reducing 50 amp (for range) to 20 amp outlet
#1
Member
Thread Starter
Join Date: Sep 2013
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Reducing 50 amp (for range) to 20 amp outlet
Wife and I decided we would like to have a gas range instead of an electric so we had the gas line run to our kitchen and bought our dream slide in gas range with convection oven. Didn't consider that our new range has a standard 3 prong cord and runs on 15-20 amps. The old range ran on 50 amps and has a 4 prong outlet, so there is no outlet that I can use close to my new oven. Can I convert the 50 amp line down to a 20 amp outlet?
#2
Welcome to the forums!
Possibly, but it's going to be a lot of work to do it. It's probably easier and safer to tap off an existing circuit or run a new one.
The power for the controls on your new all-gas (it sounds like the oven is too) range can come from one of the two 20A small appliance branch circuits that supply your countertop receptacles. You can run the wiring down and back up, if there's a basement or crawl space below your kitchen, or up and back down, if there an unfinished attic above it, to get the power where you need it.
Alternatively, you can run a new circuit from the panel. Probably still easier than converting the existing setup.
Tell us what you have now and we'll go from there.
there is no outlet that I can use close to my new oven. Can I convert the 50 amp line down to a 20 amp outlet?
The power for the controls on your new all-gas (it sounds like the oven is too) range can come from one of the two 20A small appliance branch circuits that supply your countertop receptacles. You can run the wiring down and back up, if there's a basement or crawl space below your kitchen, or up and back down, if there an unfinished attic above it, to get the power where you need it.
Alternatively, you can run a new circuit from the panel. Probably still easier than converting the existing setup.
Tell us what you have now and we'll go from there.
#3
Member
Thread Starter
Join Date: Sep 2013
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I do have a crawl space (which is separated by my garage from the circuit panel. Normally what I would do is tie into one of the existing outlets, however I believe all of them are run in serial to either each other and then to under cabinet lighting. As far as running a new circuit, that would probably be out of my skill range because how difficult my attic is to access (tall ceilings) and I would probably have to remove the drywall to run a new wire down to the circuit panel. I could possibly tie into my microwave outlet, but I believe it is recommended to have that as a designated circuit.
#4
I do have a crawl space (which is separated by my garage from the circuit panel. As far as running a new circuit, that would probably be out of my skill range because how difficult my attic is to access (tall ceilings) and I would probably have to remove the drywall to run a new wire down to the circuit panel.
I could possibly tie into my microwave outlet, but I believe it is recommended to have that as a designated circuit.
Normally what I would do is tie into one of the existing outlets, however I believe all of them are run in serial to either each other and then to under cabinet lighting.
If the required protection is provided by a couple of GFCI receptacles above the counter, I would pick the easier one of those to start from. The cable for your new receptacle will go down and back up. The box for the GFCI receptacle will be removed to give you access and replaced with an old-work box once the cable is in place. Since the new receptacle doesn't need GFCI protection, the feed for it can come from the LINE terminals on the GFCI.
#5
Member
Thread Starter
Join Date: Sep 2013
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I do have 20 amp GFCI receptacles above the counter and I would estimate that they are about 4 ft apart which is what my first thought was to tie into.
However, I still have the problem that these are daisy chained to something which in my limited knowledge means that power is coming in and there is already a feed on the line terminal (which is what I assume the daisy chain is). I assumed it was the under cabinet lighting because it was right beside it. How can I tie into the line terminals if there is already a load line on them?
The box for the GFCI receptacle will be removed to give you access and replaced with an old-work box once the cable is in place. Since the new receptacle doesn't need GFCI protection, the feed for it can come from the LINE terminals on the GFCI.
#6
How can I tie into the line terminals if there is already a load line on them?
Code note: Except for box fill nothing prevents receptacle feeding two or even three other outlets*. Feeding two is common.
However if the lights are on the circuit it is best to move them to their own circuit. Do they go out when you turn off the SAB circuits.
*Outlets as defined by the NEC.
#7
Member
Thread Starter
Join Date: Sep 2013
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
However if the lights are on the circuit it is best to move them to their own circuit. Do they go out when you turn off the SAB circuits.
Thanks for your help!!!
(Anybody need an electric range

#8
I do have 20 amp GFCI receptacles above the counter and I would estimate that they are about 4 ft apart which is what my first thought was to tie into.
However, I still have the problem that these are daisy chained to something which in my limited knowledge means that power is coming in and there is already a feed on the line terminal (which is what I assume the daisy chain is).
I assumed it was the under cabinet lighting because it was right beside it.
Originally Posted by ray2047
Do [your countertop lights] go out when you turn off [either of] the SAB circuits?
How can I tie into the line terminals if there is already a load line on them?
Originally Posted by ray2047
With most GFCIs you can... put two wires on each terminal.
Everything here should be part of a 20A circuit, so only use 12AWG wiring.
Last edited by Nashkat1; 09-17-13 at 08:32 PM.
#9
I do have 20 amp GFCI receptacles above the counter
#10
Member
Thread Starter
Join Date: Sep 2013
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
First let me say that I appreciate all the replies. I am learning a lot (granted I look like an idiot in the process, but that is part of learning). Had the opportunity today to pull out the other GFCI receptacle. It is also attached to something else (not sure what), so I am back to the pigtail option. As I mentioned before each of the GFCI receptacles are connected to two other outlets on the opposite side of my kitchen.
The work box is attached to a stud behind the tile back splash, so I am not sure how to remove the work box to put a deeper one in.
From this statement I am assuming there are no code violations with 3 outlets being fed by the receptacle. However, I assume this will increase the likelihood of tripping the breaker.
Best way is pigtails. With most GFCIs you can usually put two wires on each terminal. You do have to watch box fill so you use a deep old work box.
Code note: Except for box fill nothing prevents receptacle feeding two or even three other outlets*. Feeding two is common.
#11
It is also attached to something else (not sure what), so I am back to the pigtail option.
#12
It is probably nailed to the stud. Cut the nails by running a Sawzall between the box and the stud. (Use a wrecking blade If you don't have a Sawzall buy a wrecking blade and wrap the end with duct tape to make a handle for using it as a hand saw.