I'm planning the electrical work for the kitchen, and would appreciate some advice on what to do. I have 6 circuits that I need to route from the panel to the kitchen, which is about 60ft.
1x 50A (240V)
1x 30A (240V)
4x 20A (120V)
My original plan was to run THHN in 2 EMT conduits (1" + 3/4"). The main headache is the 50A circuit (I hate thick wires!), which I think needs 6AWG.
But, in reviewing derating and fill tables, it appears that I might do better (save a bunch of effort and wires), if I just do a subpanel close to the kitchen.
Plan #1: Individual circuits
The 1" conduit would carry the two 240V circuits:
If I go with this, does anyone see anything wrong with this design?
Plan #2: Subpanel
It then occurred to me that if I had to run 6AWG anyway, I might be able to get away with just that for *all* the circuits if I just put them on a subpanel. If I don't have to derate at all, I think 6AWG THHN is good for 75A. I'd run them to a subpanel, with a 70A breaker at the main.
Is this workable?
I think 70A is sufficient for all these circuits since most of them are really overkill for what they're used for. One concern is that my main panel already feeds another 60A subpanel to somewhere else. Is it permissible to add another 70A subpanel in this case?
Thanks a lot for any advice!
Cheers.
1x 50A (240V)
1x 30A (240V)
4x 20A (120V)
My original plan was to run THHN in 2 EMT conduits (1" + 3/4"). The main headache is the 50A circuit (I hate thick wires!), which I think needs 6AWG.
But, in reviewing derating and fill tables, it appears that I might do better (save a bunch of effort and wires), if I just do a subpanel close to the kitchen.
Plan #1: Individual circuits
The 1" conduit would carry the two 240V circuits:
- 4x 6AWG (2 hot + neutral + ground)
- 3x 10AWG (2 hot + neutral)
- 9x 12AWG (4 hot + 4 neutral + ground)
If I go with this, does anyone see anything wrong with this design?
Plan #2: Subpanel
It then occurred to me that if I had to run 6AWG anyway, I might be able to get away with just that for *all* the circuits if I just put them on a subpanel. If I don't have to derate at all, I think 6AWG THHN is good for 75A. I'd run them to a subpanel, with a 70A breaker at the main.
Is this workable?
I think 70A is sufficient for all these circuits since most of them are really overkill for what they're used for. One concern is that my main panel already feeds another 60A subpanel to somewhere else. Is it permissible to add another 70A subpanel in this case?
Thanks a lot for any advice!
Cheers.
#2
You would need to do a load calculation to see if the 70 amp feeder is large enough. I don't think it is.
If you use 12-3 you only need two runs back to the panel plus the 30 and 50 amp runs.
If you use 12-3 you only need two runs back to the panel plus the 30 and 50 amp runs.
#3
Forum Topic Moderator
I'm not a big fan of remote-located subpanels in residential situations. I find that it gets confusing as to where a circuit terminates for a savings of a few feet of wire.
I would probably run NM-B for all the circuits and ditch the EMT plan. Granted, EMT will look all nice and clean, but it'll probably be covered up anyway. As pcboss pointed out, running 4 cables 60' seems like the way to go.
As for your question though, you can add another subpanel if you want. But the kitchen is a high-draw location. I wouldn't want to risk tripping a breaker when cooking Thanksgiving dinner.
I would probably run NM-B for all the circuits and ditch the EMT plan. Granted, EMT will look all nice and clean, but it'll probably be covered up anyway. As pcboss pointed out, running 4 cables 60' seems like the way to go.
As for your question though, you can add another subpanel if you want. But the kitchen is a high-draw location. I wouldn't want to risk tripping a breaker when cooking Thanksgiving dinner.

#4
Member
Thread Starter
Join Date: Sep 2008
Posts: 104
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks, guys! I was a bit hesitant about the subpanel too, because of the high load. I'd like to run NM-B, but I don't think I can do that over most of that route (~60ft), since it has to go through an unfinished garage, and an accessible crawl space*.
I used an online load calculator and it came up with an amperage of 51A.
And just to make sure I'm understanding everything correctly, is it true that I can use 6AWG for 75A (and 12AWG for 30A), if I only have 3 CCC in a conduit?
* I've never figured out how code applies to my crawl space because it's *very* accessible. My house is split-level, so you can literally walk from the garage into the crawl space (it's ~4ft high), and I use it for storage. There are some old lights in the crawl space whose circuits were routed in EMT, but I'd love it if code lets me run romex.
I used an online load calculator and it came up with an amperage of 51A.
And just to make sure I'm understanding everything correctly, is it true that I can use 6AWG for 75A (and 12AWG for 30A), if I only have 3 CCC in a conduit?
* I've never figured out how code applies to my crawl space because it's *very* accessible. My house is split-level, so you can literally walk from the garage into the crawl space (it's ~4ft high), and I use it for storage. There are some old lights in the crawl space whose circuits were routed in EMT, but I'd love it if code lets me run romex.
#6
And just to make sure I'm understanding everything correctly, is it true that I can use 6AWG for 75A (and 12AWG for 30A), if I only have 3 CCC in a conduit?
I've never figured out how code applies to my crawl space because it's *very* accessible. My house is split-level, so you can literally walk from the garage into the crawl space (it's ~4ft high), and I use it for storage. There are some old lights in the crawl space whose circuits were routed in EMT, but I'd love it if code lets me run romex.
#7
Granted, EMT will look all nice and clean, but it'll probably be covered up anyway.
#8
Member
Thread Starter
Join Date: Sep 2008
Posts: 104
Upvotes: 0
Received 0 Upvotes
on
0 Posts
#12 is limited to 20 amps by Article 240. The #6 is only good for 60 amps.
But what about #6 THHN? Going by the same table 310.16, 90C #6 is rated for 75A. So assuming that no temperature adjustment is required, is there some other adjustment factor, similar to 240.4(D), that I'm missing?
#9
But what about #6 THHN? Going by the same table 310.16, 90C #6 is rated for 75A. So assuming that no temperature adjustment is required, is there some other adjustment factor, similar to 240.4(D), that I'm missing?
You must use the values in the 60[SUP]o[/SUP]C. column for standard ampacities and conductor sizing. Joe said
I wouldn't protect the #6 any higher than 60 amps
#11
The 90 degree column is where you start to derate from. The end number cannot be higher than the 60 or 75 degree column.
#12
you never really get to use the 90C non-derated limits anyway.
IOW, we didn't need to derate.