Panel to Sub
House was built in 1959. I have a 100 amp service and panel in the house. My issue is that I was going to put a 220 30 amp breaker in the garage subpanel. When I went to do this I notice that the garage panel is only feed from one leg of the service to the house. When I opened up the panel in the house I see that the leg to the garage isnt feed from a breaker but is connected to one of the lugs. Also the airconditioner is being feed in the same way. Is that right?
The garage does have a 30 amp shut off/disconnect. I am not an electrician, but am handy, and that doesnt seem right to me. So based on that to get 220 out to the garage I would have to run another leg from my panel to the garage also?
The garage does have a 30 amp shut off/disconnect. I am not an electrician, but am handy, and that doesnt seem right to me. So based on that to get 220 out to the garage I would have to run another leg from my panel to the garage also?
#2
If you mean the the lugs on the main beaker and if the panel has the first overcurrent protection device fixing this major code violation is not a DIY job..
!20 comes from a neutral and a single pole breaker and 240 comes from a 2 pole breaker. 120/240 which is what your garage needs comes from a 2 pole breaker and a neutral. Look at the subpanels here: http://www.doityourself.com/forum/el...-diagrams.html to get a beter idea.
First though we need to know if this is an attached garage or a detached garage and if it is supplied by cable or conduit.
!20 comes from a neutral and a single pole breaker and 240 comes from a 2 pole breaker. 120/240 which is what your garage needs comes from a 2 pole breaker and a neutral. Look at the subpanels here: http://www.doityourself.com/forum/el...-diagrams.html to get a beter idea.
First though we need to know if this is an attached garage or a detached garage and if it is supplied by cable or conduit.
Last edited by ray2047; 10-03-13 at 08:22 PM. Reason: Misread original post.
#3
When I opened up the panel in the house I see that the leg to the garage isnt feed from a breaker but is connected to one of the lugs. Also the airconditioner is being feed in the same way. Is that right?

#4
Original content of post was based on a misread and I retract it. Double lugging is so wrong my mind just didn't process it correctly when I first read it. Some comments below are based on my original thought you meant the neutral bar.
Last edited by ray2047; 10-03-13 at 08:28 PM.
#5
I hope you are right ray, but that's not the way I read it. The OP has a 120 volt service to his garage and then what bothered me was this.
It sure sounds like a double lugged main to me.
I see that the leg to the garage isnt feed from a breaker but is connected to one of the lugs.
#6
When I opened up the panel in the house I see that the leg to the garage isnt feed from a breaker but is connected to one of the lugs. Also the airconditioner is being feed in the same way. Is that right?
sticking with Joe's interpretation for now, I also agree with his advice:
Originally Posted by CasualJoe
No, that isn't right and is a fire hazard, those circuits have absolutely NO overcurrent protection. If you had a short develop, the wire would have to burn through to clear the fault and would probably set your house on fire in the process. A fuse or circuit breaker is a pre-determined weak sacrificial link to safely open the circuit in the event of overload or a fault. It is very important to get those circuits removed from the panel lugs immediately.
Tech Note: The feed lugs in a main distribution panel with the first overcurrent protection device in it are always hot unless there is a power outage. Working with those is not a DIY job.
And we still need the answers to Ray's questions.
#7
I see that the leg to the garage isn't feed from a breaker but is connected to one of the lugs.