Can you paint NM-B wire?
I'm sure this has been asked before, but I haven't found a definite answer yet. Can you paint NM-B wire indoors?
#4
NM-b should be run in the wall. You can not run it on the face of a wall. You can sleeve it in conduit. If it is an uninterrupted run of conduit from the panel to a junction box NM-b can be used but best practice is individual conductors such as THHN/THWN.
Yes conduit can be painted. If looks are important you might want to use a surface raceway such as Wiremold.
Yes conduit can be painted. If looks are important you might want to use a surface raceway such as Wiremold.
#6
Yes....you can use the conduit as a mechanical raceway.
You would physically have to measure the width of 8-2 cable but it may need to be in a 1" pipe.
You would physically have to measure the width of 8-2 cable but it may need to be in a 1" pipe.
#11
Well pump. 240v only. Might add something else later.
Can I staple/clip/tie the wire in the basement along the joists in the open(there are no walls) or must I use conduit there too?
#12
Member
Thread Starter
Join Date: Sep 2013
Location: USA
Posts: 39
Upvotes: 0
Received 0 Upvotes
on
0 Posts
If you might add something that will use 120V you need to run 8-3/G to a subpanel. Why do you need to use 8AWG? What is the amp draw of the pump and how long is the run?
#13
The pump only draws max 6 amps. About a 220 ft run.
I might add a 4000 watt max 240v heater and maybe a 240v hot water heater later.
What you want to do is best done using at least a 240 only subpanel but for only slightly more in cable cost you can future proof it by using 8-3 and a 120/240 subpanel.
#14
Member
Thread Starter
Join Date: Sep 2013
Location: USA
Posts: 39
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Then it should be on a 15 amp breaker and the #8 is way over size and may not even fit the breaker.
#15
I'm not going to add anything that will use 120v.
I might add a 4000 watt max 240v heater and maybe a 240v hot water heater later. The pump only draws max 6 amps. About a 220 ft run. The heater would just be for backup to my propane heat if I'm gone for a few days in the winter. Then I'd shut the pump off. So they would probably never be running at the same time. But I figured if I did run all three at the same time that 8 gauge with a 40 amp time delay fuse in the Range box feeding the subpanel would handle it. All 3 would have their separate circuit breakers in the subpanel.
This sounds like a set of appliances on the other side of the basement from your panel, but 220' sounds like a run to a separate structure. Is it?
I figured if I did run all three at the same time that 8 gauge with a 40 amp time delay fuse in the Range box feeding the subpanel would handle it.

#16
Member
Thread Starter
Join Date: Sep 2013
Location: USA
Posts: 39
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Really? Ever? No light or receptacle?
This sounds like a set of appliances on the other side of the basement from your panel, but 220' sounds like a run to a separate structure. Is it?
OK. I'm confused. The Range box? What is that?
#17
it's a short run (maybe 15 ft.) from my fuse panel to a subpanel in the basement. It's a very small house.
About a 220 ft run.
I have an older fuse panel (probably 1950's) that has a MAIN fuse block and a RANGE fuse block and 4 120v fuses. I have nothing running off the 240v RANGE block so I'm running a #8 wire protected by a 40 amp time delay to a subpanel in the basement which will have circuit breakers matched to whatever it feeds.
#19
It's about a 220 ft. run from the subpanel to the submersible pump in the well, which will be fed by 12-2 wire.
#20
Member
Thread Starter
Join Date: Sep 2013
Location: USA
Posts: 39
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Yes....you can use the conduit as a mechanical raceway.
You would physically have to measure the width of 8-2 cable but it may need to be in a 1" pipe.
You would physically have to measure the width of 8-2 cable but it may need to be in a 1" pipe.
#21
No, it's a short run (maybe 15 ft.) from my fuse panel to a subpanel in the basement. It's a very small house.
How deep is the pump?
#22
Member
Thread Starter
Join Date: Sep 2013
Location: USA
Posts: 39
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Well, the main reason I didn't go with 8-3 is because I've really got to bend the cable and get it through the 3/8 clamp connector without wrecking to much of the drywall. Using the 8-2 was hard enough. If I used 8-3 I might even have to go to the next size clamp connector and a bigger knockout hole. This would involve tearing a bigger hole in the drywall. It's a flush mounted older panel and I have to dig a little bit of the drywall out to access a side knockout. That's why I decided to go with 8-2. The main thing I want this cable for is to run my 240v pump
#25
Well, the main reason I didn't go with 8-3 is because I've really got to bend the cable and get it through the 3/8 clamp connector without wrecking to much of the drywall. Using the 8-2 was hard enough.
Small complaint here you made this more confusing then it had to be by saying you were running the cable for a pump instead of for a subpanel. Mentioning a 6 amp pump and 8-2 initially confused the issue. Had you said subpanel from the beginning the replies might have been different.
#28
Member
Thread Starter
Join Date: Sep 2013
Location: USA
Posts: 39
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Small complaint here you made this more confusing then it had to be by saying you were running the cable for a pump instead of for a subpanel. Mentioning a 6 amp pump and 8-2 initially confused the issue. Had you said subpanel from the beginning the replies might have been different.
#29
Member
Thread Starter
Join Date: Sep 2013
Location: USA
Posts: 39
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Instead of cable just cut an opening in the Sheetrock for a 4x4 box flush with the wall and connect it to the panel with a short nipple. Add an extension ring to the junction box and run conduit all the way to the new subpanel. Then use THHN/THWN individual wires between the two panels.
#30
Sorry I look at a lot of posts. I usually don't remember who wrote what.
Yes, except for the ground. The ground could be #10. You could use a single gang box if you can find one that has 3/4" holes and did not splice in the box.
If you were running #8 NM-B, would you run #8 THHN?l