Ground Rod

Reply

  #1  
Old 10-11-13, 09:37 AM
Member
Thread Starter
Join Date: Aug 2012
Posts: 11
Received 0 Votes on 0 Posts
Ground Rod

So, i've completed an installation of a 100 amp subpanel in a detatached garage.. and i'm trying to sort out the ground rods... My question is how many do i need? I can not seem to locate the requirement for the number of rods in the 2011 NEC? 1 or 2? or the wire size...
thanks
 
Sponsored Links
  #2  
Old 10-11-13, 09:43 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,106
Received 30 Votes on 24 Posts
I'd just use one with #6 copper wire, I prefer bare 7 strand.
 
  #3  
Old 10-15-13, 04:03 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 8,470
Received 1 Vote on 1 Post
The number of ground rods needed is not specified in the code, only the requirement for a low-impedance path to ground. The means needed to meet that requirement is a local decision based on the conductivity of the soils in your area.

Ask your inspector.
 
  #4  
Old 10-15-13, 05:57 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,962
Received 34 Votes on 29 Posts
Unless you can prove less than 25 ohms resistance on one rod you will need another one. If using a Ufer ground, you do not need any rods.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: