Ground Rod


  #1  
Old 10-11-13, 08:37 AM
S
Member
Thread Starter
Join Date: Aug 2012
Posts: 11
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ground Rod

So, i've completed an installation of a 100 amp subpanel in a detatached garage.. and i'm trying to sort out the ground rods... My question is how many do i need? I can not seem to locate the requirement for the number of rods in the 2011 NEC? 1 or 2? or the wire size...
thanks
 
  #2  
Old 10-11-13, 08:43 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,827
Received 178 Upvotes on 161 Posts
I'd just use one with #6 copper wire, I prefer bare 7 strand.
 
  #3  
Old 10-15-13, 03:03 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 7,458
Upvotes: 0
Received 5 Upvotes on 4 Posts
The number of ground rods needed is not specified in the code, only the requirement for a low-impedance path to ground. The means needed to meet that requirement is a local decision based on the conductivity of the soils in your area.

Ask your inspector.
 
  #4  
Old 10-15-13, 04:57 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,923
Received 177 Upvotes on 155 Posts
Unless you can prove less than 25 ohms resistance on one rod you will need another one. If using a Ufer ground, you do not need any rods.
 
 