6/3 UF in 1" liquid tight hot tub connection

Help, I'm just a girl trying to pull 6/3 UF through 1" liquid tight. Dawn dish soap doesn't seem to be enough lubrication for the job, any tips? Also, I have 160' run from my panel to the disconnect done in the 6/3 UF buried 18" deep without conduit. However, from the disconnect to the spa what is the best wire scenario to use? 6/3 UF in liquid tight or 4 separate THHN in liquid tight?
Thank you!
 
  #2  
Old 10-17-13, 07:55 AM
W
Member
Join Date: Jun 2008
Location: VA.
Posts: 765
Upvotes: 0
Received 1 Upvote on 1 Post
Replace the UF with individual conductors.

Uf or any cable assembly outside is illegal. The ground wire has to be insulated.

Edit: you can't even use the UF to feed the disconnect.
 
  #3  
Old 10-17-13, 08:22 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,905
Received 168 Upvotes on 147 Posts
The UF could be in used for any interior portion of the wiring. Once outside the ground must be insulated.

You have a lot of work to redo.
 
  #4  
Old 10-17-13, 09:18 AM
B
Member
Thread Starter
Join Date: Oct 2013
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Okay, now anyone have tips on pulling the wire through the conduit. Local store is out of wire lube. Tried binding the wires together and using dawn to aid in the pulling. Slowly pushing from one end and pulling from the other. Any tips are greatly appreciated.
 
  #5  
Old 10-17-13, 09:41 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,884
Received 710 Upvotes on 603 Posts
3 #6 wires plus a ground should go into a 1" liquid tight, even if it is the non metallic kind. Are you trying to push through a 90 degree fitting? Of so you need to remove the fitting.

Try using a strong string or a fish tape. Run the fish tape in, attach the wires to the tape, and with the help of a friend, pull the wires in while pushing from the other end. Keep the flex straight and keep the wires so they don't overlap/twist.
 
  #6  
Old 10-17-13, 10:00 AM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 7,458
Upvotes: 0
Received 5 Upvotes on 4 Posts
4 separate THHN in liquid tight?
Conductors installed in conduit outside must be rated as water resistant. You need to use THWN. Most individual conductors are dual rated (THHN/THWN) so you may already have them. The green insulated ground wire can be #10 AWG.

The requirement for the insulated ground should only apply from the disconnect to the tub.
 
  #7  
Old 10-17-13, 10:13 AM
B
Member
Thread Starter
Join Date: Oct 2013
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thank you for all your responses. Just left a professional electric supply house. Got 1 1/4" non metallic flex with fittings. I'm leaving the 6/3 UF as is and running the THWN from the disconnect to the tub. Can't wait to get it up and running.
 
  #8  
Old 10-17-13, 11:57 AM
W
Member
Join Date: Jun 2008
Location: VA.
Posts: 765
Upvotes: 0
Received 1 Upvote on 1 Post
The requirement for the insulated ground should only apply from the disconnect to the tub.
For outdoor installations, Part II of 680 applies. Outside branch circuits must have an insulated copper EGC no smaller than #12.
 
  #9  
Old 10-17-13, 03:08 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,905
Received 168 Upvotes on 147 Posts
Many tub instructions call for a full sized #6 ground.

The conductors in the conduit need to have the proper insulation colors, two black, a white and a green. You could also use a black and a red instead of two blacks.
 
  #10  
Old 10-17-13, 03:31 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 7,458
Upvotes: 0
Received 5 Upvotes on 4 Posts
The part from the house to the disconnect is buried UF. It's designed for use outdoors, feeding whatever load. However, Article 680 requires an insulated ground for pools and hot tubs. The exterior UF needs to be replaced.

Pcboss has got the info on the wires in the conduit.
 

Last edited by pcboss; 10-17-13 at 03:39 PM. Reason: added note
 