I have a 240v 7.5 kw heater in my garage. It has an internal high voltage thermostat. I can't set a specific temperature though. It just has a dial with dots on it. I want to replace the internal thermostat with a relay controlled by a wall mounted low voltage thermostat.

I know that I need to bypass the internal thermostat and put in a 40 amp relay with a 24v coil as well as a 110v to 24v transformer to send power to the thermostat.

So my problem/question, there is no common wire coming into the heater. All I have is two 110v legs (black & red) and a ground (green). So how do I wire in a transformer without a common wire? I know that I could send it down the ground, but for obvious reasons I don't want to do that.

Also, will I need a common wire for the relay as well?

If somebody could point me in the right direction I would be very appreciative.

I've attached two pic's in case that might help....
 
Attached Images   
  #2  
Old 10-21-13, 05:51 AM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,499
Received 92 Upvotes on 84 Posts
  #3  
Old 10-21-13, 06:13 AM
S
Member
Thread Starter
Join Date: Oct 2013
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
and I just put a wire nut on the white (common wire) coming off that transformer?
 
  #4  
Old 10-21-13, 06:54 AM
W
Member
Join Date: Jun 2008
Location: VA.
Posts: 765
Upvotes: 0
Received 1 Upvote on 1 Post
Is there any reason why you wouldn't just get a line voltage T-stat and use it to break one leg of the coil for your existing contactor?
 
  #5  
Old 10-21-13, 07:04 AM
S
Member
Thread Starter
Join Date: Oct 2013
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
I already ran a low voltage thermostat wire from where I want the thermostat to be, to the heater. The whole garage is finished and I don't want to redo drywall or have conduit or wires on the outside of the wall.
 
  #6  
Old 10-21-13, 07:09 AM
W
Member
Join Date: Jun 2008
Location: VA.
Posts: 765
Upvotes: 0
Received 1 Upvote on 1 Post
Get the 240-24 volt transformer then a single pole contactor or a relay, with a 24 volt coil, use the contactor to break one leg of your existing contactor coil or replace your existing contactor with a 24 volt one.
 
  #7  
Old 10-21-13, 09:20 AM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,499
Received 92 Upvotes on 84 Posts
With that transformer use white and orange to L1 and L2 as you have 240 volts. Cap the black and red wires on the primary side.
 
  #8  
Old 10-24-13, 07:32 PM
S
Member
Thread Starter
Join Date: Oct 2013
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
got it installed and it works great. Thanks guys!
 
 