Amperage drop/wire size

Need to figure amperage drop/wire size, on buried cable for 70 amps over 200 ft. Using aluminum. HELP!!
 
Sponsored Links
  #2  
Old 11-05-13, 12:47 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 8,470
Welcome to the forums!

Amperage doesn't drop with distance. Voltage does. The conservative value is to limit the voltage drop to 3% or less. The calculation for the wire size needed to do that is based on distance, load and wiring method. The information we need is:
  • Is the distance from breaker to load exactly 200 ft?
  • What is the maximum load? So you need a foll 70A?
  • Are you planning to pull individual aluminum conductors in buried conduit, or some other method?
  • Is single-phase 240V correct?
 