How critical of a situation is this?
I have a loaded 15A breaker in basement. 14AWG wiring.
Washing Machine label says 10A =1200W
Currently running 7 can lights with 10W CFL's. =70
3x26W CFL overhead lights
1x20 CFL overhead lights
And there is another unused outlet available.
Im sure there is an acceptable percentage of 1800W (15A).... have I passed this? Obviously with the use of incansescents this would be pushed past the limits of the breaker already.
I know I need a dedicated line for washer, but how quickly do I have to get this done?
I have a loaded 15A breaker in basement. 14AWG wiring.
Washing Machine label says 10A =1200W
Currently running 7 can lights with 10W CFL's. =70
3x26W CFL overhead lights
1x20 CFL overhead lights
And there is another unused outlet available.
Im sure there is an acceptable percentage of 1800W (15A).... have I passed this? Obviously with the use of incansescents this would be pushed past the limits of the breaker already.
I know I need a dedicated line for washer, but how quickly do I have to get this done?
#6
That would be 80% of rated capacity, but continuous is considered 3 or more hours.
Right now, with 168W of continuous load from the CFLs and the non-continuous load from the washing machine, you're not pushing the circuit's limits - 1440W for continuous and 1800W for non-continuous. (1800 - 1200 = 600 * .8 = 480 - 168 = 312W available.)
#8
A rule of thumb is that if the hard wired items rated wattages add up to more than half of the circuit's breakered (intermittent) wattage, those items should be in their own circuit.
Your actual usage is well below the circuit rating. You can procrastinate on adding more circuits so long as you are careful about what you plug in and when you turn each item on, so you don't trip the breaker.
When you do upgrade, don't forget that the circuit intended for the washing machine must be 20 amp (12 gauge wire) and have receptacles only in the laundry area (and no lights on it).
Your actual usage is well below the circuit rating. You can procrastinate on adding more circuits so long as you are careful about what you plug in and when you turn each item on, so you don't trip the breaker.
When you do upgrade, don't forget that the circuit intended for the washing machine must be 20 amp (12 gauge wire) and have receptacles only in the laundry area (and no lights on it).
#9
80% is the rule of thumb, but the NEC does permit full loading
210.20 Overcurrent Protection.
(A) Continuous and Noncontinuous Loads. Where a
branch circuit supplies continuous loads or any combination
of continuous and noncontinuous loads, the rating
of the overcurrent device shall not be less than the noncontinuous
load plus 125 percent of the continuous load.
(A) Continuous and Noncontinuous Loads. Where a
branch circuit supplies continuous loads or any combination
of continuous and noncontinuous loads, the rating
of the overcurrent device shall not be less than the noncontinuous
load plus 125 percent of the continuous load.
Originally Posted by CasualJoe
continuous is considered 3 or more hours.
Originally Posted by Nashkat1
All of the lights should probably be considered as continuous. In addition, the load is calculated using the maximum rated wattage of the fixtures, not the wattage of the installed bulbs.
Originally Posted by Nashkat1
with 168W of continuous load from the CFLs and the noncontinuous load from the washing machine, you're not pushing the circuit's limits - 1440W for continuous and 1800W for noncontinuous. (1800 - 1200 = 600 * .8 = 480 - 168 = 312W available.)
I like the logic of the NEC's formula better, and I like the one I use for easier calculation. You just have to keep in mind which type of load you're getting an answer for.
[Note: Maybe I like mine better and think it's easier to use just because I'm used to it.