Outdoor Receptical Help Please
Received 0 Votes
Hi guys,
I am looking to install a new outdoor receptacle for a roof ice melt system.
The max draw is 20 amps.
The panel (power source) is outdoors about 50 feet from where I want the new receptacle located. The receptacle will be located under a soffit basically out of the weather, but exposed to outdoor conditions.
I'd like to route the wire outside.
I have a spare 20 amp breaker.
Here are my questions:
can you guys recommend a receptacle. I assume I need to use a GFCI outlet or GFCI breaker.
what size and type of wire should I use
does the wire need to be in a conduit
I'm sure I have not asked all the questions, but thought this thread could get the discussion started.
Thank you for your help.
Bob-
Bob-
Received 0 Votes
Good stuff here. Thank you.
I need to check on the amperage. I thought I read that the max draw was 20 amps so I figured a 20 amp circuit would be sufficient. Is this not true?
Thanks for the data on wires, conduit and receptacle.
Great site!
Bob-
Great site!
Bob-
Circuits are rated to run at 80% of their maximum. Hence, a 20 amp circuit maxes out at a continuous 16 amp load and would therefore not suffice if you actually needed 20 amps.
Even if it is not continuous it would be a crap shoot at best. If it has a standard 120 volt plug it is less than 15 amps. If 20 amp plug probably more then 15.
Image source: Freson's Hardware