Trouble with 3-way switches
#1
Member
Thread Starter
Trouble with 3-way switches
HI,
New member here.
I can't make it work!
I moved into an older home recently and am trying to replace some switches to a more modern look. I have a 3-way circuit controlling a ceiling light fixture. One switch is a 3-way toggle type, and the other is a 3-way dimmer (Lutron C.L digital dimmer).
The electrical box where the dimmer is going to be, has a 3-wire cable (red, white, & black). The black is hot.
The electrical box where the non-dimmer 3-way is, has a red & white coming from a 3-wire cable (red white and black, not sure where the black is going), and a black wire coming from a 2-wire Romex. I'm assuming for the moment that the black from the Romex cable is going to the light fixture, but not sure. None of the wires from this electrical box are hot.
Thanks for the help.
Bill

New member here.
I can't make it work!
I moved into an older home recently and am trying to replace some switches to a more modern look. I have a 3-way circuit controlling a ceiling light fixture. One switch is a 3-way toggle type, and the other is a 3-way dimmer (Lutron C.L digital dimmer).
The electrical box where the dimmer is going to be, has a 3-wire cable (red, white, & black). The black is hot.
The electrical box where the non-dimmer 3-way is, has a red & white coming from a 3-wire cable (red white and black, not sure where the black is going), and a black wire coming from a 2-wire Romex. I'm assuming for the moment that the black from the Romex cable is going to the light fixture, but not sure. None of the wires from this electrical box are hot.
Thanks for the help.
Bill


#2
Did you mark the common wire when you changed out the switch. You can't go by the location of the screw on the old switch. It can vary with manufacturer. You must go by screw color. The common being the odd coloured screw, usually dark gray.
#3
Member
Thread Starter
Unfortunately I didn't mark the common.
Here is some additional info I just found.
I ran a wire on the floor between each box and utilized an ohm meter.
Non-dimmer red >>>>>>>>>>>>>>Dimmer White
Non-dimmer White>>>>>>>>>>>>>Dimmer Red
None-dimmer Black>>>>>>>>>>>> Dimmer Black>>>>>>>>Light Fixture
None Dimmer Black>>>>>>>>HOT
Here is some additional info I just found.
I ran a wire on the floor between each box and utilized an ohm meter.
Non-dimmer red >>>>>>>>>>>>>>Dimmer White
Non-dimmer White>>>>>>>>>>>>>Dimmer Red
None-dimmer Black>>>>>>>>>>>> Dimmer Black>>>>>>>>Light Fixture
None Dimmer Black>>>>>>>>HOT
#4
The hot should go to one common. The black to the light should go to the common of the other switch.
Red and black of the 3-conductor cable between the switches are probably travelers and need to go to the traveler screws on the switches.
White of the 2-conductor power in cable and white of 2-conductor cable to light goes to white of the 3-conductor cable between the switches.
If the above doesn't work substitute a regular 3-way switch for the dimmer. Once it is working and we know the wiring is correct we can try to get the dimmer to work.
Red and black of the 3-conductor cable between the switches are probably travelers and need to go to the traveler screws on the switches.
White of the 2-conductor power in cable and white of 2-conductor cable to light goes to white of the 3-conductor cable between the switches.
One switch is a 3-way toggle type, and the other is a 3-way dimmer (Lutron C.L digital dimmer).
#5
Member
Thread Starter
Wired with non-dimmer switch and it worked
I wired the black to the black screw on the dimmer switch (it's not marked common). I wired the black wire in the none-dimmer switch black screw (which is marked common). The white and red wires were wired on the remaining 2 screws since I thought they were travelers. Again, the light works only if the non-dimmer switch I switched in one position. In the other position, nothing works. I reversed the red and white wires, and got the same results.
As you suggested, I swapped out the dimmer with a non-dimmer and it works now.
The 1st photo shows the permanent 3-way the black wire from the 2-conductor cable is wired to the common. The other two wires (red and white) are to the travelers.

The 2nd photo shows the swapped out 3-way (non-dimmer). From the 3-conductor cable, the black (HOT) is wired to the common. The red and white are wired to the travelers.

The 3rd photo is the dimmer I want to swap out with the 2nd photo
As you suggested, I swapped out the dimmer with a non-dimmer and it works now.
The 1st photo shows the permanent 3-way the black wire from the 2-conductor cable is wired to the common. The other two wires (red and white) are to the travelers.

The 2nd photo shows the swapped out 3-way (non-dimmer). From the 3-conductor cable, the black (HOT) is wired to the common. The red and white are wired to the travelers.

The 3rd photo is the dimmer I want to swap out with the 2nd photo

Last edited by onthegulf; 11-12-13 at 11:35 AM.
#6
The white and red wires were wired on the remaining 2 screws since I thought they were travelers.
Originally Posted by ray2047
White of the 2-conductor power in cable and white of 2-conductor cable to light goes to white of the 3-conductor cable between the switches.
The electrical box where the dimmer is going to be, has a 3-wire cable (red, white, & black). The black is hot.
and that the
None Dimmer Black>>>>>>>>HOT
and that the
None Dimmer Black>>>>>>>>HOT
#7
The white and red wires were wired on the remaining 2 screws since I thought they were travelers.
- The hot should go to one common.
- The black to the light should go to the common of the other switch.
- Red and black of the 3-conductor cable between the switches are probably travelers and need to go to the traveler screws on the switches.
- White of the 2-conductor power in cable and white of 2-conductor cable to light goes to white of the 3-conductor cable between the switches.
The puzzling thing is that you said that
The electrical box where the dimmer is going to be, has a 3-wire cable (red, white, & black). The black is hot.
The electrical box where the dimmer is going to be, has a 3-wire cable (red, white, & black). The black is hot.
#8
Member
Thread Starter
Hi Nash,
I used both non-contact & multi-meter.
To answer your questions.
Neither boxes have a black HOT going to several different switches. The box with the 3 switches clearly has a 2-conductor Romex cable. Only the black wire was used on the previous switch. A red and white wire coming from a 3-conductor cable were used on the remaining terminals.
The 2 switch box has a 3-conductor cable feeding the old switch. The black is HOT. This is also very clear to see.
I just sent Ray an update with photos, please check it out.
I used both non-contact & multi-meter.
To answer your questions.
Neither boxes have a black HOT going to several different switches. The box with the 3 switches clearly has a 2-conductor Romex cable. Only the black wire was used on the previous switch. A red and white wire coming from a 3-conductor cable were used on the remaining terminals.
The 2 switch box has a 3-conductor cable feeding the old switch. The black is HOT. This is also very clear to see.
I just sent Ray an update with photos, please check it out.
#9
I just sent Ray an update with photos, please check it out.
The 2 switch box has a 3-conductor cable feeding the old switch. The black is HOT. This is also very clear to see.
#11
The 3rd photo is the dimmer I want to swap out with the 2nd photo
#13
Member
Thread Starter
Lutron AMCL-153MH-WH
The package says: "Works with companion dimmers or a standard 3-way switch, single pole, 3-way, or multi-location.
The package says: "Works with companion dimmers or a standard 3-way switch, single pole, 3-way, or multi-location.
#14
Lutron AMCL-153MH-WH
The package says: "Works with companion dimmers or a standard 3-way switch, single pole, 3-way, or multi-location.
What do the instructions say? Can you post a link to those?
Using a multimeter to determine the common terminal might be possible, and might help.
#15
The box with the 3 switches clearly has a 2-conductor Romex cable. Only the black wire was used on the previous switch. A red and white wire coming from a 3-conductor cable were used on the remaining terminals.
#18
Member
Thread Starter
Yes, sorry, it is a MACL
http://www.lutron.com/TechnicalDocum...ry/369613a.pdf
http://www.lutron.com/TechnicalDocum...y/0301629b.pdf
I'll need some instructions / help on how to determine the common on this switch using a multi-meter.
Thanks
http://www.lutron.com/TechnicalDocum...ry/369613a.pdf
http://www.lutron.com/TechnicalDocum...y/0301629b.pdf
I'll need some instructions / help on how to determine the common on this switch using a multi-meter.
Thanks
#20
The instructions you linked to for the MACL-153M don't match your device. They're for a dimmer that has four wires to connect, not three screws.
Double-check the model # of the control you have. It should be stamped into the yoke or faceplate.
A control that only has three terminals, with one of those marked as ground, won't be a 3-way control and won't have a common terminal.
Double-check the model # of the control you have. It should be stamped into the yoke or faceplate.
I'll need some instructions / help on how to determine the common on this switch using a multi-meter.
#21
Member
Thread Starter
Look at page 2, 5b Two-Locations. Those are the same instructions that came in the package that the switch was in. The part number was confirmed on the switch which has 3-screws + the ground.
(I've always used a 3-connector switch with no problems on new construction. The switches I'm replacing on this project both had 3-connector switches. One switch was a dimmer, one was a none-dimmer). The two 3-way none-dimmmers currently working are both 3-connector switches.
Lutron MACL-153MH-WH
The package says: "Works with companion dimmers or a standard 3-way switch, single pole, 3-way, or multi-location.
(I've always used a 3-connector switch with no problems on new construction. The switches I'm replacing on this project both had 3-connector switches. One switch was a dimmer, one was a none-dimmer). The two 3-way none-dimmmers currently working are both 3-connector switches.
Lutron MACL-153MH-WH
The package says: "Works with companion dimmers or a standard 3-way switch, single pole, 3-way, or multi-location.
#23
Just a quick question..... that dimmer works in conjunction with a standard three way switch BUT the wiring of the standard three way switch is not standard. At the standard switch end..... two of the wires get connected together to one terminal and the third wire goes to the odd colored screw.
After wiring it this way.....which is in the instructions..... you may have to program the dimmer which is also on the instructions.
I just went thru this with a tech at Lutron. Great techs working there.
After wiring it this way.....which is in the instructions..... you may have to program the dimmer which is also on the instructions.
I just went thru this with a tech at Lutron. Great techs working there.

#24
Look at page 2, 5b Two-Locations.
5b - Two-Location
Wiring the Dimmer:
Hm. OK, I don't think I read it carefully enough. I see that they've marked one of the terminals "blur" and they ro go on to talk about screws.Wiring the Dimmer:
- Connect the green ground wire on the Dimmer to the bare copper or green ground wire in the wallbox. (See Important Note 3 on reverse side)
- Connect the tagged wire removed from the switch to the black screw terminal on the Dimmer.
- Connect one of the remaining wires removed from the switch to the brass screw terminal on the Dimmer.
- Connect the remaining wire removed from the switch (note wire color) to the blue screw terminal on the Dimmer.
"Important Note 3" tells you to tag the wire connected to the common terminal on the old switch. So did you tag that black wire and follow these instructions? Didn't that work?
#26
Connect the remaining wire removed from the switch (note wire color) to the blue screw terminal on the Dimmer
I had to wire some of these in a customers house. Did you ever try to read the Lutron instructions.

And then the programming step which is not listed as "for proper three way operation" but is required. I talked to a great tech at Lutron who is also a member here.
#27
this noted wire color is used a certain way at the standard switch end