Is it ok to move an outlet this way?
#1
Member
Thread Starter
Join Date: May 2007
Location: USA
Posts: 41
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Is it ok to move an outlet this way?
Hi All,
I have an outlet in the garage ceiling that I need to move to the wall. Instead of dealing with running it through the wall, I thought I'd add an outlet extender to the existing outlet then run conduit over to the wall and add the outlet.
Is there anything wrong with doing that?
Thanks!
I have an outlet in the garage ceiling that I need to move to the wall. Instead of dealing with running it through the wall, I thought I'd add an outlet extender to the existing outlet then run conduit over to the wall and add the outlet.
Is there anything wrong with doing that?
Thanks!
#2
No restriction unless the receptacle is a dedicated circuit for a garage door opener. I wouldn't see a problem with it. Make sure you secure your conduit properly and use the proper connections.
#3
Member
Thread Starter
Join Date: May 2007
Location: USA
Posts: 41
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks Larry.
It is the garage door opener outlet, but it is being moved to the wall for the new garage door opener, is that ok?
Also, I can't use romex in the conduit correct? If not, what do you call the wire I should use so I can research, and how would I determine the correct size? I don't want to have to trust the guy at the home store, Thanks!
It is the garage door opener outlet, but it is being moved to the wall for the new garage door opener, is that ok?
Also, I can't use romex in the conduit correct? If not, what do you call the wire I should use so I can research, and how would I determine the correct size? I don't want to have to trust the guy at the home store, Thanks!
#4
You can use romex in conduit, but it can be a pain to install it. If you can keep the bends to just one or two you should be Ok with 1/2" EMT or 3/4" PVC conduit. Wire size should be the same as what it is in the original box.
If you want to use individual wires (best option IMO) you need THHN. If you use PVC you are required to pull in a Green/bare ground wire.
If you want to use individual wires (best option IMO) you need THHN. If you use PVC you are required to pull in a Green/bare ground wire.
#6
Also, I can't use romex in the conduit correct? If not, what do you call the wire I should use so I can research, and how would I determine the correct size? I don't want to have to trust the guy at the home store, Thanks!
#8
what about this bit "It is the garage door opener outlet, but it is being moved to the wall for the new garage door opener, is that ok?"
#11
Member
Thread Starter
Join Date: May 2007
Location: USA
Posts: 41
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I hadn't seen a wall mount either, but apparently they are common for large heavy single doors.
Thanks!
Assuming it already does, will I be able to extend that like I'm trying to do then use a GFI outlet?
It's best to use individual conductors such as Type THHN in conduit. Use 12 awg for a 20 amp circuit or 14 awg for a 15 amp circuit.
It will also need GFI protection.
#14
Member
Thread Starter
Join Date: May 2007
Location: USA
Posts: 41
Upvotes: 0
Received 0 Upvotes
on
0 Posts
So long as the GFCI can be operated standing on the floor, yes.
#15
currently it's 10ft up on the ceiling... was that not correct or would some other method have been used?
The ceiling-mounted receptacles for garage door openers must be provided with GFCI protection, and the TEST and RESET controls for that protection must be accessible - which means no ladder. Feeding those receptacles from a GFCI receptacle mounted at standard height in the garage or from a GFCI breaker are two commonly used methods.
#16
Member
Thread Starter
Join Date: May 2007
Location: USA
Posts: 41
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thank you, but you stated it wasn't done correctly, and then said:
That could be how it's done now right?? I'm not there to see, but I would assume it was up to code, it's a newer home.
If it was done correctly, is it still ok for me to extend it as per my original plan?
Feeding those receptacles from a GFCI receptacle mounted at standard height in the garage or from a GFCI breaker are two commonly used methods.
If it was done correctly, is it still ok for me to extend it as per my original plan?
#19
That could be how it's done now right?? I'm not there to see, but I would assume it was up to code, it's a newer home.
How high will the receptacle be at the new location?