Question Sub Panel has 120V and 240V Circuits

I have installed 2 sub panels. One at my detached garage, and the other at my detached office. My question is: Do I need a grounding rod at the point of each of the 2 sub panels?
 
Sponsored Links
  #2  
Old 11-25-13, 03:46 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,595
Panels in detached structures require a grounding electrode system unless they are only served by a single circuit.
 
  #3  
Old 11-25-13, 04:31 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,066
Both a ground rod, GEC, and an EGC. You do have four wires to the panels don't you?
 