Unfinished bsmnt: max distance from NM in ceiling joists to junction box on wall

I知 adding circuits to an unfinished basement. I知 using NM wherever I move through/along the ceiling joists. When I want to move vertically down the exposed, poured-foundation wall, I知 adding a box, pigtailing to THHN, and running the THHN through EMT. I知 having trouble finding the maximum distance from the top of the wall that I can mount the box. That is, it would be silly to mount the box three feet below the top of the wall and let the NM run down that length to it. But am I being overly pedantic in making sure the top of the box is as high as the top of the wall? Or can it be within six inches of the top? My concern is with drilling into the concrete that close to its edge耀ecuring the boxes would mean drilling within an inch or so of the top of the wall.

Thanks!
 
  #2  
Old 12-01-13, 09:34 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,130
Received 3,616 Upvotes on 3,242 Posts
Six inches from the top of the wall should be fine. The NM should be pretty well protected with only the top 6" exposed on the wall.
 
  #3  
Old 12-03-13, 09:49 PM
R
Member
Thread Starter
Join Date: Mar 2006
Posts: 10
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks. I'll be paying for a (voluntary) inspection once everything is all done, and this kind of echos what the inspector was telling me when I had him out for a preliminary look---when asking about a different area, he stressed the protection of the cables from snagging or hanging much more than anything else.
 
  #4  
Old 12-04-13, 04:23 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,923
Received 177 Upvotes on 155 Posts
You could just sleeve the cable in a conduit sleeve down the wall and just skip the splice.
 
  #5  
Old 12-04-13, 05:19 AM
R
Member
Thread Starter
Join Date: Mar 2006
Posts: 10
Upvotes: 0
Received 0 Upvotes on 0 Posts
I was under the impression that I could only run NM cable through conduit if the wires were properly labelled/stamped (I'm out of my element terminology-wise). That is, when I strip off some of the sheathing of the NM cable the insulation of the inside wires do not carry any markings. Hence I went with a splice to THHN that is individually rated (again, my apologies for sloppy use of words).

Is this a hyper-technical reading of the code? A mistaken reading of the code? If it's technically part of code, is it a safety factor or to make it easier for the next person working?

Work/effort aside, am I actually introducing a weak point (e.g. risk of sheathed cable inside conduit versus an added splice))?
 
  #6  
Old 12-04-13, 06:21 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
I was under the impression that I could only run NM cable through conduit if the wires were properly labelled/stamped (I'm out of my element terminology-wise).
That applies if the sheath is removed and only the wires are use.

I went with a splice to THHN that is individually rated
Always best practice but not a code violation to put NM in conduit, just harder to pull. In fact it is a good practice and sometimes required to use short sections of non continuous conduit as a protective sleeve.
 
  #7  
Old 12-04-13, 06:28 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,827
Received 178 Upvotes on 161 Posts
I was under the impression that I could only run NM cable through conduit if the wires were properly labelled/stamped (I'm out of my element terminology-wise).
NM cables can be run through a short length of EMT conduit as a sleeve for protection. When you do this, the open end of the EMT needs to have a bushing to protect against cutting the cables. A simple drive-on bushing is typically the best way to go. DO NOT strip the sheathing from the cables till the cables enter the box.

Arlington EMT100-100 EMT Insulating Conduit Bushing for Electrical Metal Tubing, White, 1-Inch, 100-Pack - Amazon.com
 
  #8  
Old 12-04-13, 07:04 AM
canuk's Avatar
Member
Join Date: Sep 2013
Posts: 257
Upvotes: 0
Received 0 Upvotes on 0 Posts
Work/effort aside, am I actually introducing a weak point (e.g. risk of sheathed cable inside conduit versus an added splice))?
No. Actually the junction you proposed would be the *weak* point --- so to speak.
 
 