14g on 20a lighting old home
#1
Member
Thread Starter
Join Date: Nov 2013
Posts: 304
Upvotes: 0
Received 0 Upvotes
on
0 Posts
14g on 20a lighting old home
Husband was looking at our Kitchen circuit. The lighting and the outlets are both on it. Connected to the 20A breaker is 12g wire. All of the outlets are fed with 12g wire. However, he noticed that the switch legs to the lights and switches is 14g.
We know the code requirement but are wondering if this situation was ever allowed. This house was built in the mid 50's.
Is this a big safety concern? Is it common to see 14g on a 20a on lighting in an old home?
We know the code requirement but are wondering if this situation was ever allowed. This house was built in the mid 50's.
Is this a big safety concern? Is it common to see 14g on a 20a on lighting in an old home?
#2
Connected to the 20A breaker is 12g wire. All of the outlets are fed with 12g wire. However, he noticed that the switch legs to the lights and switches is 14g.
#3
I don't know if this was ever allowed. I don't remember this practice being used when I started in the early 80's. This would not be allowed now.
If only the lights are fed with #14 it is probably less of an issue since the load from the fixtures is a known quantity. If the #14 was in the middle of the circuit I would be more concerned.
I too would suggest changing this if a remodel of the area is done. Many light fixtures call for 90 degree rated insulation anyway.
If only the lights are fed with #14 it is probably less of an issue since the load from the fixtures is a known quantity. If the #14 was in the middle of the circuit I would be more concerned.
I too would suggest changing this if a remodel of the area is done. Many light fixtures call for 90 degree rated insulation anyway.
#4
If only the lights are fed with #14 it is probably less of an issue since the load from the fixtures is a known quantity.
#5
Member
Thread Starter
Join Date: Nov 2013
Posts: 304
Upvotes: 0
Received 0 Upvotes
on
0 Posts
CASUAL JOE
From what I recall, that was only allowed on switchlegs and switchloops on 20 amp circuits, nowhere else. I think that's also what the OP says her husband has found.
From what I recall, that was only allowed on switchlegs and switchloops on 20 amp circuits, nowhere else. I think that's also what the OP says her husband has found.
FWIW: The constant load is a 6.5A fridge. There is also a microwave and coffee pot that are used periodically. There is a ceiling fan and about 100W of lights total on that circuit.
So do you think its common to find #14 on a 20A as described?
If no kitchen remodelling/rewiring is planned, do you think this is something safe to leave as is indefinetly?
#6
If you can find where the first #14 for lighting connection originates you may be able to run a new 15 amp circuit to that point and disconnect the current feed. That could mean minimal or no opening of the wall to fish new cable. You have less load on the SABC receptacles and code compliant wire for the lights.
#7
So do you think its common to find #14 on a 20A as described?
If no kitchen remodelling/rewiring is planned, do you think this is something safe to leave as is indefinetly?
If no kitchen remodelling/rewiring is planned, do you think this is something safe to leave as is indefinetly?
#8
Member
Thread Starter
Join Date: Nov 2013
Posts: 304
Upvotes: 0
Received 0 Upvotes
on
0 Posts
CASUAL JOE
Unless you are having problems tripping the breaker, I believe I'd just leave it alone.
Unless you are having problems tripping the breaker, I believe I'd just leave it alone.
----------
If the 20A breaker is connected to #12 and the outlets are connected to #12 is it safe to assume the #14 at the lighting would not be in the middle of that? Meaning, the loads on the outlets are not passing thru #14 lighting and then back to the panel on the #12.... does my description makes any sense???
#9
If the 20A breaker is connected to #12 and the outlets are connected to #12 is it safe to assume the #14 at the lighting would not be in the middle of that? Meaning, the loads on the outlets are not passing thru #14 lighting and then back to the panel on the #12.... does my description makes any sense???