Sauna Breaker
Old 12-11-13, 06:41 AM
Gen
Gen is offline
Sauna Breaker
I have a sauna that's going to be installed. The unit info states using 42 amps.
I want to know breaker size to install also--will 2 pole 40A suffice?
And will 8-3 wire be enough? Thanks in advance.
Old 12-11-13, 06:46 AM
CasualJoe's Avatar
Assuming you are planning on using NM-B cable (aka romex), 8-3 is only rated for 40 amps. I would use 6-3 NM-B cable and a 60 amp breaker.
Old 12-11-13, 06:56 AM
Gen
Gen is offline
OK great I get it about the wire. I want to better understand the breaker....my thinking is...and this is not a challenge, rather to understand....if the unit is rated at 42A and I put in a 60A breaker, aren't I allowing the thing to possibly too pull much power which would be not desireable??
Old 12-11-13, 07:06 AM
CasualJoe's Avatar
The maximum current draw is 42 amps regardless of the breaker, the beaker does not control that. The major load of a sauna is the heater. I wouldn't load the breaker more than 80% of it's capacity. For a 60 amp breaker that would be 48 amps. You may want to read through the installation instructions as well and see what they recommend.
Old 12-11-13, 07:35 AM
pcboss's Avatar
For example, if you were to install a 100 watt lightbulb on a 15 amp circuit it will only draw less than one amp, not the 15 the breaker would allow.
Old 12-11-13, 07:45 AM
Gen
Gen is offline
OK thanks very much for the replies!