Is this acceptable?

Reply

  #1  
Old 12-22-13, 04:30 PM
Member
Thread Starter
Join Date: Sep 2013
Posts: 10
Is this acceptable?

Trying to connect to panel in garage. Sheetrock in garage is 5/8's. I cannot find a 4 inch j box with 5/8 set back. J box and first extension ring get me flush with Sheetrock. Second extension ring used to come out of wall and into 3/4 conduit. I am running power to basement. Running romex from panel to j box then connect to THHN in conduit into basement. 9 total wires in conduit - 8 current carrying conductors and one ground wire. 4 circuits in basement - 3 20 amp, 1 15 amp. Suggestions welcomed.

Happy Holidays everyone.
 
Attached Images  
Sponsored Links
  #2  
Old 12-22-13, 05:39 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,589
You could bend an offset in the conduit to reach the second extension ring and then install the proper depth plaster ring.
 
  #3  
Old 12-22-13, 05:52 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 46,182
I thought the same thing as the Boss.

Name:  pipe.jpg
Views: 219
Size:  36.3 KB
 
  #4  
Old 12-22-13, 07:14 PM
Mr.Awesome's Avatar
Member
Join Date: Oct 2013
Location: Canada, SK
Posts: 576
If he is just using this as a junction box (no device installed), wouldn't a mud ring just make it more difficult to work inside of the box in the future?
 
  #5  
Old 12-22-13, 07:21 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 46,182
A two gang mud ring would be the best choice.
 
  #6  
Old 12-22-13, 07:53 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,284
Just as a note most of the NM connectors, like the ones you have used, are rated for two cables each.

BTW - Welcome to the forums!
 
  #7  
Old 12-22-13, 08:24 PM
Member
Thread Starter
Join Date: Sep 2013
Posts: 10
Thanks everyone. I was reading 314.22 and it is vague about the number of extensions rings that can be used. It doesn't say I can't add two rings to one box. I imagine the conductors have to extend 6 inches out of second ring as if a device were attached? To answer Mr. Awesome - it's just a j box, no devices.
 
  #8  
Old 12-22-13, 09:40 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 8,470
To answer Mr. Awesome - it's just a j box, no devices.
Then you don't have to install a mud ring. You can install a 1900 blank on the first extension ting if you want to.

If you'd rather install a mud ring and a finish blank cover, you can use a flat (no rise) mud ring.
 