GFCI - Downstream Receptacles only 50 V
#1
Member
Thread Starter
Join Date: Dec 2013
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
GFCI - Downstream Receptacles only 50 V
My GFCI was tripping every one to two weeks (I suspect by a compact fridge on the downstream circuit). I would reset and things would work fine. Now the fridge is inoperable and downstream receptacles are showing about 50 to 55 V according to my multimeter, though the outlets on the GFCI receptacle show the full 120 V. The indicator light is not illuminated. I removed the fridge from the circuit (it was the only item) and no luck with resets. Any thoughts on a fix? Simple GFCI replacement? Thanks.
-Tom
-Tom
#2
Welcome to the forums.
I find the indicators all but useless. When you install them for a living..... some have a red light, some have a green light, some lights come on when GFI is normal, some come on when it trips and some come on when GFI is defective.
Try checking the voltage from the small slot to ground. The GFI may trip depending on the meter you use. Also check from the large slot to ground.
I would doubt the GFI receptacle is defective.
I find the indicators all but useless. When you install them for a living..... some have a red light, some have a green light, some lights come on when GFI is normal, some come on when it trips and some come on when GFI is defective.
Try checking the voltage from the small slot to ground. The GFI may trip depending on the meter you use. Also check from the large slot to ground.
I would doubt the GFI receptacle is defective.
#3
Double check to be sure that the live power feed for this GFCI receptacle is connected to the GFCI terminals labeled "line." Cables connected to downstream receptacles to be GFCI protectedl are connected to the GFCI terminals labeled "load."
Something is definitely wrong (probably a wiring mistake) if the GFCI receptacle itself has a different voltage from other receptacles that GFCI also protects.
Something is definitely wrong (probably a wiring mistake) if the GFCI receptacle itself has a different voltage from other receptacles that GFCI also protects.
#4
Member
Thread Starter
Join Date: Dec 2013
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Good questions, so here's some additional info:
GFCI receptacle:
small to large slot = 120V
small to ground = 120V
large to ground = 0V
downstream receptacles:
small to large slot = ~51V
small to ground = 120V
large to ground = ~56V
T
GFCI receptacle:
small to large slot = 120V
small to ground = 120V
large to ground = 0V
downstream receptacles:
small to large slot = ~51V
small to ground = 120V
large to ground = ~56V
T
#5
The 56v from the large slot to ground tells us that you have an open neutral. It should be 0v.
#6
Member
Join Date: Dec 2013
Posts: 122
Upvotes: 0
Received 0 Upvotes
on
0 Posts
downstream receptacles:
small to large slot = ~51V
small to ground = 120V
large to ground = ~56V
small to large slot = ~51V
small to ground = 120V
large to ground = ~56V
If you are using a digital multimeter the readings below 90 volts are probably just induced voltages.
#7
You know you have hot to ground - 120 volts. You also know you only have hot to neutral - 51 volts.
I agree with PJ, you have an open/loose neutral connection after the GFCI device and before the downstream receptacles. I've seen this happen many times.
The 56v from the large slot to ground tells us that you have an open neutral.