Fluorescents and grounding

Reply

  #1  
Old 01-17-14, 08:48 AM
Member
Thread Starter
Join Date: Nov 2013
Posts: 365
Received 0 Votes on 0 Posts
Fluorescents and grounding

Was doing some cleaning and noticed the green grounding screw inside my metal fluorescent fixture is not used.

We have conduit. The fixture is connected to the conduit with a connector and a knockout. I assume we are mechanically grounded as I have read about here.

There is no grounding wire coming from the ballast.

So is this a bad thing? Will my light not function properly if that green screw isn't used?
 
Sponsored Links
  #2  
Old 01-17-14, 09:02 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,001
Received 40 Votes on 35 Posts
Sounds like your metal conduit is providing the ground.
 
  #3  
Old 01-17-14, 09:39 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,301
Received 43 Votes on 35 Posts
There is no grounding wire coming from the ballast.
But I'd bet the metal case of the ballast is screwed to the housing.
 
  #4  
Old 01-17-14, 10:25 AM
Member
Thread Starter
Join Date: Nov 2013
Posts: 365
Received 0 Votes on 0 Posts
It is screwed to the housing.

I found the installation instructions and it says to make sure its grounded otherwise it can cause a shock hazard, overheating, premature bulb failure or a non functioning light....

I understand shock hazard but what about the rest? Please explain....
 
  #5  
Old 01-17-14, 11:41 AM
Member
Join Date: Oct 2013
Location: United States
Posts: 235
Received 0 Votes on 0 Posts
Fluorescent Lamps

Your conduit is the ground for your fixture. If the fixture was not grounded it most likely would not light properly as a grounded surface is needed along the length of the lamp. Hear is a good explanation of the need for the grounded reflector:
"Newer rapid start ballast designs provide filament power windings within the ballast; these rapidly and continuously warm the filaments/cathodes using low-voltage AC. No inductive voltage spike is produced for starting, so the lamps must be mounted near a grounded (earthed) reflector to allow the glow discharge to propagate through the tube and initiate the arc discharge. In some lamps a grounded "starting aid" strip is attached to the outside of the lamp glass."
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: