sub panel from house 200 amp breaker box

I have a detached shed 180 feet from actual main breaker box. want to use a 100 amp breaker and if a #6 can be used.

If I go with #8 can a 60 Amp breaker be used?
 
  #2  
Old 01-17-14, 03:22 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
#8 is only good for 40 amps but at 180 feet if your load is great enough you may need to go to #6 on a 40 amp breaker.
 
  #3  
Old 01-17-14, 03:25 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 7,458
Upvotes: 0
Received 6 Upvotes on 5 Posts
Welcome to the forums!

What will the connected load in the shed be?
 
  #4  
Old 01-17-14, 03:53 PM
M
Member
Join Date: Mar 2009
Location: Northern Virginia
Posts: 3,914
Received 27 Upvotes on 21 Posts
I hate to bring the subject of voltage drop up again, but it really hasn't been resolved. Is 5% a general rule of thumb, or does NEC explicity set restrictions on the amount of allowable drop? 180 feet is a pretty good run. #8 copper will give the OP a DC drop of 16.8V (14%) at full load!
 
  #5  
Old 01-17-14, 05:55 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,874
Received 185 Upvotes on 166 Posts
Is 5% a general rule of thumb, or does NEC explicity set restrictions on the amount of allowable drop?
Voltage drop is not specified by the NEC, but 3% maximum for a feeder is suggested; 5% maximum for both feeder and branch circuit is recommended.

Don't Let Voltage Drop Get Your System Down | Code Basics content from Electrical Construction & Maintenance (EC&M) Magazine

As far as I know, this is not something that is revised by each code panel every three years.
 
  #6  
Old 01-18-14, 05:43 AM
M
Member
Join Date: Mar 2009
Location: Northern Virginia
Posts: 3,914
Received 27 Upvotes on 21 Posts
Voltage drop is not specified by the NEC, but 3% maximum for a feeder is suggested; 5% maximum for both feeder and branch circuit is recommended.
That being said, it's probably fine to use the expected maximum current draw when calculating voltage drop, as opposed to the subpanel rating. However, it would be wise to use the panel rating to ensure voltage drop is a non-issue. Better to run a slightly larger gauge to be sure.
 
  #7  
Old 01-18-14, 07:12 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,874
Received 185 Upvotes on 166 Posts
Better to run a slightly larger gauge to be sure.
Spoken like a true engineer!
 
 