Grounding ungrounded outlets
#1
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 2
Received 0 Votes
on
0 Posts
Grounding ungrounded outlets
Hi all!
Can I ground an ungrounded outlet feed from a
sub-panel by running a ground wire from a
grounded outlet which is feed from the main panel.
(Note the sub panel originally was the main before someone installed a new one.)
Can I ground an ungrounded outlet feed from a
sub-panel by running a ground wire from a
grounded outlet which is feed from the main panel.
(Note the sub panel originally was the main before someone installed a new one.)
#2
Can I ground an ungrounded outlet feed from a
sub-panel by running a ground wire from a
grounded outlet which is feed from the main panel.
sub-panel by running a ground wire from a
grounded outlet which is feed from the main panel.
#4
By code the new ground can be connected to the main ground of the source panel at any suitable place within five feet of the panel. Best to go into the panel but connecting to the nipple between the panels would probably be code compliant.
#5
There should be one or two grounding conductors coming out of the main panel to go to ground rods or a water pipe. You can connect the new grounding conductor to any of those w/in 5' of the panel.
Your new grounding conductor needs to be green insulated wire, not bare copper.