Sub Panel Questions
#1
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Sub Panel Questions
I am planning to set up a sub panel in my mother's garage. The house has a 125Amp service panel with spare space to put a breaker. The 21' x 22' garage is mostly detached but the roofs of the two structures connect via a dog trot (15 feet long by 8 feet wide) with an enclosed ceiling. The service panel is on the exterior of the building. The circuits my mother needs to set up the garage as an art studio are: one lighting circuit for 6 dual-bulb, 4-foot flourescent fixtures, one electrical recepticles circuit, one circuit for sprinkler control and two dedicated circuits for a couple of small split pack AC units. The cable path distance from the service panel to the proposed sub panel location is approximaely 100 feet.
My plan is to set up a lug panel with 8 spaces in the garage, feed it with a 60A breaker from the service panel, use NM-B 6/3 cable and run the cable up into the attic and over to the sub panel in the garage.
I've read a lot of good information on sub panels on this forum but still have a few questions about this specific installation:
1) The service panel is surface mounted on the brick on the outside wall of the house. the hole in the brick where all the branch circuits are run into the house is pretty full. Can I run the cable feeding the sub panel up from the service panel in conduit on the outside of the building through the roof soffit above and then stapled in the attic the rest of the way to the sub panel in the garage?
2) I consider the garage to be detached but it is connected to the house using the same roof. Does this application need a separage ground rod?
3) The split pack A/C units are pretty small and only need a 15A 110VAC circuit each. Can I just provide them each with an fused or unfused 30A disconnect (smallest I find). If fused, I can change the fuses to 15A.
4) If I use one of these disconnects, since they are for a 220VAC circuit, do I only break the one hot leg or do I also break the neutral through the disconnect?
Thanks for any advice on this.
My plan is to set up a lug panel with 8 spaces in the garage, feed it with a 60A breaker from the service panel, use NM-B 6/3 cable and run the cable up into the attic and over to the sub panel in the garage.
I've read a lot of good information on sub panels on this forum but still have a few questions about this specific installation:
1) The service panel is surface mounted on the brick on the outside wall of the house. the hole in the brick where all the branch circuits are run into the house is pretty full. Can I run the cable feeding the sub panel up from the service panel in conduit on the outside of the building through the roof soffit above and then stapled in the attic the rest of the way to the sub panel in the garage?
2) I consider the garage to be detached but it is connected to the house using the same roof. Does this application need a separage ground rod?
3) The split pack A/C units are pretty small and only need a 15A 110VAC circuit each. Can I just provide them each with an fused or unfused 30A disconnect (smallest I find). If fused, I can change the fuses to 15A.
4) If I use one of these disconnects, since they are for a 220VAC circuit, do I only break the one hot leg or do I also break the neutral through the disconnect?
Thanks for any advice on this.
#2
Member
Join Date: Oct 2013
Location: United States
Posts: 189
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Sub Panel Question
The service panel is surface mounted on the brick on the outside wall of the house. the hole in the brick where all the branch circuits are run into the house is pretty full. Can I run the cable feeding the sub panel up from the service panel in conduit on the outside of the building through the roof soffit
300.9 Raceways in Wet Locations Abovegrade. Where
raceways are installed in wet locations abovegrade, the interior
of these raceways shall be considered to be a wet location.
310.8(C) Lists the insulations allowed in wet locations.
334.12(B) NM cable cannot be used in damp or wet locations.
You need to install your EMT from the panel to the attic and use #6THWN-CU conductors 2-Blk 1-White ( need to buy the #6 neutral with white insulation) only conductors larger than #6 can be identified using white tape(200.6) You can install a NEMA-1 junction box in the attic and splice you single-conductors to you NMB cable conductors. The EMT can serve as the ground up to the J-Box but you need to bond the ground conductor in you cable to the J-Box.
#3
run the cable up into the attic and over to the sub panel in the garage.
#4
Can I run the cable feeding the sub panel up from the service panel in conduit on the outside of the building through the roof soffit above and then stapled in the attic the rest of the way to the sub panel in the garage?
Since the breezeway has a ceiling, I'd say that you're good to use NM-B from the attic to the garage subpanel, but ask your local jurisdiction - your inspector - to be sure.
I consider the garage to be detached but it is connected to the house using the same roof. Does this application need a separage ground rod?
The split pack A/C units are pretty small and only need a 15A 110VAC circuit each. Can I just provide them each with an fused or unfused 30A disconnect (smallest I find). If fused, I can change the fuses to 15A.
do I only break the one hot leg or do I also break the neutral through the disconnect?
#5
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks to all - this is great information.
bahtah - I was going to use rigid rather than EMT since it was outside exposed and only a small straight vertical run. If I can use EMT outside it would be easier. Thanks for the information about how to keep this within NEC.
CasualJoe - There is attic space all the way to the garage. The dog trot connecting the house to the garage is about 8' wide by 15' long and it is an enclosed roof so makes a small attic crawl space connection to the garage.
Nashkat - Thanks, I searching the permit process online now. It's in Harris County, Texas and their site does not make it easy. I'll probably call and speak to someone in the permits office.
bahtah - I was going to use rigid rather than EMT since it was outside exposed and only a small straight vertical run. If I can use EMT outside it would be easier. Thanks for the information about how to keep this within NEC.
CasualJoe - There is attic space all the way to the garage. The dog trot connecting the house to the garage is about 8' wide by 15' long and it is an enclosed roof so makes a small attic crawl space connection to the garage.
Nashkat - Thanks, I searching the permit process online now. It's in Harris County, Texas and their site does not make it easy. I'll probably call and speak to someone in the permits office.
#6
I was going to use rigid rather than EMT
3) The split pack A/C units are pretty small and only need a 15A 110VAC circuit each. Can I just provide them each with an fused or unfused 30A disconnect (smallest I find). If fused, I can change the fuses to 15A
#7
I searching the permit process online now. It's in Harris County, Texas and their site does not make it easy.
I was going to use rigid rather than EMT since it was outside exposed and only a small straight vertical run.
#8
It's in Harris County, Texas and their site does not make it easy.
#9
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Apologies for the delay in responding. I am working on the framing to get the garage setup to turn into an art studio. It was easier framing and remodeling when I was a kid than now in my 50's. Good chance to teach my kids a little about building though.
Thanks again for the help. I'm getting closer to the point I want to do the electrical. In answer to your questions:
It is Harris County but outside of the city of Houston to the North. Cypress area north of FM 1960. Whether or not they do much inspection in Harris County, do you know if a home owner can pull a permit from the county?
It has a hip roof with a relatively steep pitch. It looks like I can use a 45-degree sweep on the conduit as it enters through the soffit and then extend into a box fastened to a rafter
Thanks for the suggestion. In this particular case, my mother plans to put these two split packs on either side of the back wall so they will probably be separated about 18 feet apart. I will likely use the horsepower rated 20A switch idea that Nashkat1 suggested
I've spliced cables in juntion boxes before, but never a feed to a panel. What are the options for the splices and the best methods.
Thanks again for all the help.
Thanks again for the help. I'm getting closer to the point I want to do the electrical. In answer to your questions:
ray2047
County or city? If Houston a permit must be pulled and only a master electrician can pull the permit. I'm not familiar with Pasadena but I do recall they have strict code enforcement. If county there is very little inspection.
County or city? If Houston a permit must be pulled and only a master electrician can pull the permit. I'm not familiar with Pasadena but I do recall they have strict code enforcement. If county there is very little inspection.
Nashkat1
How will you get from the top of the vertical run into the J-box where the individual conductors can be spliced to the conductors in the cable?
How will you get from the top of the vertical run into the J-box where the individual conductors can be spliced to the conductors in the cable?
Tolyn Ironhand
Run one 3 wire cable (14/3) and install a 2 pole 15 amp breaker. This will give you the 2 - 120 volt, 15 amp circuits you need for the A/C units. The two circuits will share the neutral.
Run one 3 wire cable (14/3) and install a 2 pole 15 amp breaker. This will give you the 2 - 120 volt, 15 amp circuits you need for the A/C units. The two circuits will share the neutral.
bahtah
You need to install your EMT from the panel to the attic and use #6THWN-CU conductors 2-Blk 1-White ( need to buy the #6 neutral with white insulation) only conductors larger than #6 can be identified using white tape(200.6) You can install a NEMA-1 junction box in the attic and splice you single-conductors to you NMB cable conductors. The EMT can serve as the ground up to the J-Box but you need to bond the ground conductor in you cable to the J-Box.
You need to install your EMT from the panel to the attic and use #6THWN-CU conductors 2-Blk 1-White ( need to buy the #6 neutral with white insulation) only conductors larger than #6 can be identified using white tape(200.6) You can install a NEMA-1 junction box in the attic and splice you single-conductors to you NMB cable conductors. The EMT can serve as the ground up to the J-Box but you need to bond the ground conductor in you cable to the J-Box.
Thanks again for all the help.
#10
I've spliced cables in juntion boxes before, but never a feed to a panel. What are the options for the splices and the best methods.