AC wiring question

My model unit is 4TTR4060C1.
Right now this unit is running on a double pole 30 amp breaker and 10/2 wire. Should this unit be on a 60 amp breaker on 6/2 wire ?
Thanks for your help.
#2
Minimum circuit ampacity is 36 amps, and maximum fuse size is 60 amps.
Your wire size should be at least #8 copper and a fuse/circuit breaker no larger than 60 amps. However, your fuse/breaker can't be bigger than the wires are rated for.
If you run:
#8 Romex, it can only be on a 40 amp max.
#8 in conduit it can be on a 50 amp max.
#6 romex can be on a 50 or 60 amp.
#6 in conduit it can be on a 60 amp max.
Welcome to the forums!
Your wire size should be at least #8 copper and a fuse/circuit breaker no larger than 60 amps. However, your fuse/breaker can't be bigger than the wires are rated for.
If you run:
#8 Romex, it can only be on a 40 amp max.
#8 in conduit it can be on a 50 amp max.
#6 romex can be on a 50 or 60 amp.
#6 in conduit it can be on a 60 amp max.
Welcome to the forums!
#3
Member
However, your fuse/breaker can't be bigger than the wires are rated for.
My guess is that the compressor was swapped out with a larger unit and the installer didn't want to replace the cable. Probably other problems with the install as well.
#5
Member
Join Date: Oct 2013
Location: United States
Posts: 189
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Hvac
440.22(A) covers short-circuit and ground-fault protection. Can't exceed 175% of motor-compressor load current or branch circuit selection current which ever is greater. If that will not handle the starting current then you can increase to a max of 225%. However 440.22(C) States the device rating cannot exceed the manufactures values. So the manufactures nameplate cannot be exceeded. The branch circuit conductors must be a minimum of 125% of the motor-compressors rated load current. In addition you must meet the requirements of 440.51 and 440.52 for Motor-compressor and branch circuit overload protection. If the manufactures nameplate calls for fuse protection you must provide fuse protection. If the manufactures nameplate calls for HACR or Fuse you can use either. I think the bottom line is the branch circuit can be protected higher than the conductor rating to allow for starting current as with other motor installations and the manufacture specifies protection on the nameplate to protect the unit.
#6
The bottom line, assuming the chart provided by OP is the correct one, the branch circuit wiring should be no smaller than 8-2 NM-B cable. Since the unit is holding on a 30 amp breaker now, I'd probably put it on a 40 amp breaker with a fusible disconnect also fused at 40 amps. If the unit is not drawing FLA, there may be another problem such as a low charge.
I don't see that note on the chart provided.
Note Trane document says "fuse" but also has a note that breakers are ok.
#7
Member
A search for 4TTR4060C1 found the pdf at http://www.blue-phx.com/pdf/Trane%20...%20Product.pdf
Page 4 has footnote 2 which says "Calculated in accordance with N.E.C. Only use HACR circuit breakers or fuses."
Page 4 has footnote 2 which says "Calculated in accordance with N.E.C. Only use HACR circuit breakers or fuses."
#8
A search for 4TTR4060C1 found the pdf at http://www.blue-phx.com/pdf/Trane%20...%20Product.pdf
Page 4 has footnote 2 which says "Calculated in accordance with N.E.C. Only use HACR circuit breakers or fuses."
Page 4 has footnote 2 which says "Calculated in accordance with N.E.C. Only use HACR circuit breakers or fuses."