wiring to my barn went funky
#1
Member
Thread Starter
Join Date: Jan 2014
Location: usa
Posts: 12
Upvotes: 0
Received 0 Upvotes
on
0 Posts
wiring to my barn went funky
3 years ago i rewired my barn for 240/120 service with a new box and new wires. i used the existing wires that run from the breaker box at the pole overhead to the barn they are 4 gauge wire.everything was fine then all of a sudden one night while i was working late i saw sparks come from the outside of the building and then the some of the light bulbs blew, replace bulbs and they act like they are at half power. upon inspection the main wires coming into the building was the shorting culprit. there was not a weather head the wires just ran through the metal wall and you could see where it was shorting out. put in a weather head and ran conduit. now that everything is hooked back up the lights still act like they are at half power.
#4
Member
Thread Starter
Join Date: Jan 2014
Location: usa
Posts: 12
Upvotes: 0
Received 0 Upvotes
on
0 Posts
here is the weird thing , i measured the voltage coming in at 120v . if i have the upstairs breaker and the down stairs breaker on the upstairs lights quit and the downstairs lights go real bright. if i shut the downstairs breaker off the upstairs lights work perfect. i measured these 2 breakers and they test at 240v . these are 2 separate circuits that do not join any where. the rest of my breakers are dead no voltage at them at all .
#6
When you unhooked the feed wires going directly through the barn wall and connected them to the weatherhead, you might have reconnected the wires in the wrong order causing 240 volts to be put across one side of the barn subpanel.
#7
Member
Thread Starter
Join Date: Jan 2014
Location: usa
Posts: 12
Upvotes: 0
Received 0 Upvotes
on
0 Posts
i never disconnected it outside i unhooked at box pulled it out and fed it through the conduit. i rechecked the main wire is at 120. possible my box shorted out some how?
Last edited by marvin75; 01-27-14 at 12:48 PM.
#8
i rechecked it the main wire is at 120. possible my box shorted out some how?
Originally Posted by ray2047
You need to check for 240 volts across the subpanel's main breaker. It sounds like a dead leg more than an open neutral.
Let us know what you find with this test.
#9
upon inspection the main wires coming into the building was the shorting culprit. there was not a weather head the wires just ran through the metal wall and you could see where it was shorting out
#10
Member
Thread Starter
Join Date: Jan 2014
Location: usa
Posts: 12
Upvotes: 0
Received 0 Upvotes
on
0 Posts
ok i replaced wiring coming in and measured the voltage at all connections on the way down to the breaker box at 120 v. my box doesn't have a main breaker. i measured the legs at 240v on the left side and 120v on the right side. i even went to the pole and checked the breaker voltage there and it was at 120 each side of the breaker.(it is a 50 amp double pole breaker)
#11
measured the legs at 240v on the left side and 120v on the right side.
went to the pole and checked the breaker voltage there and it was at 120 each side of the breaker.

my box doesn't have a main breaker
Last edited by ray2047; 02-02-14 at 11:20 AM. Reason: Clarification
#12
Member
Thread Starter
Join Date: Jan 2014
Location: usa
Posts: 12
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Across the main lugs 240v . I rechecked the wires and they are hooked up right. Their is a place for a main breaker but i didn't put one in since it is on a 50 amp at pole.
#13
Across the main lugs 240v . I rechecked the wires and they are hooked up right.
measured the legs at 240v on the left side and 120v on the right side.
#14
Their is a place for a main breaker but i didn't put one in since it is on a 50 amp at pole.
Last edited by ray2047; 02-02-14 at 11:34 AM.
#15
Member
Thread Starter
Join Date: Jan 2014
Location: usa
Posts: 12
Upvotes: 0
Received 0 Upvotes
on
0 Posts
It has 12 circuits. Since there is a main box over at the pole i don't have a main in the box at the barn.the wires are connected using lugs like the picture you used as an example minus the main breaker
#16
Since there is a main box over at the pole i don't have a main in the box at the barn.the wires
So are you having the same problems with the electric at the barn? If so have you measured the voltage at the lights?
#17
Member
Thread Starter
Join Date: Jan 2014
Location: usa
Posts: 12
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I better get a main then i guess. I measured at the. Wire coming off the breaker and it was 240v i know ot should be 120v. I measure at the lights to see and keep you posted.
#18
I measured at the. Wire coming off the breaker and it was 240v i know ot should be 120v.
#19
Member
Thread Starter
Join Date: Jan 2014
Location: usa
Posts: 12
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I went back down and measured at the light 120v ... as soon as i turn the upstairs on it jumps to 240v. I even swapped the breakers to the other leg and got same results. I try to get pictures as soon as i can.
#20
I went back down and measured at the light 120v ... as soon as i turn the upstairs on it jumps to 240v.
- Is the voltage between the upstairs neutral to ground ~0 volts?
- Is the upstairs voltage ~120 volts neutral to hot?
- Is the upstairs voltage black to ground 120 volts?
Will await pictures.
I measured at the. Wire coming off the breaker and it was 240v i know ot should be 120v.

#21
Member
Thread Starter
Join Date: Jan 2014
Location: usa
Posts: 12
Upvotes: 0
Received 0 Upvotes
on
0 Posts
At the pole the breaker looks just like that. If i hold probes on screws i get 120v. If i go to the barn and measure at the lugs the main wires go into 240v . If i measure the single pole breaker my lights are on i get 240v if the upstairs light switch is on, shut it off and i get 120v at that single pole breaker.
#22
Member
Join Date: Jan 2014
Location: USA
Posts: 630
Upvotes: 0
Received 0 Upvotes
on
0 Posts
First of all , If he has a 2 pole 50 amp Circuit Breaker " at the pole " feeding the barn , NEC does not require a main in the barn loadcenter . Local codes may or may not .
There is an upstairs and a downstairs , in the barn ?
Please send a photo of your barn loadcenter .
When you turn on thing / lite on and it changes the voltage of something else , it REALLY sounds like you lost your neutral & are running off of the earth ground .
Either the ground rod , metal building steel , cold water ground , etc. . Reguardless , it is not safe ! :-(
Just a thought , measure between the incoming neutral and earth ground . This is not conclusive , if the neutral is bonded to earth ground . But try it , with various lites and / or other loads turned on .
I repeat , it sounds like a bad neutral . Could be at the " pole " which is feeding the barn or at the loadcenter that has the 2 P 50 amp CB ?
God bless
Wyr
There is an upstairs and a downstairs , in the barn ?
Please send a photo of your barn loadcenter .
When you turn on thing / lite on and it changes the voltage of something else , it REALLY sounds like you lost your neutral & are running off of the earth ground .
Either the ground rod , metal building steel , cold water ground , etc. . Reguardless , it is not safe ! :-(
Just a thought , measure between the incoming neutral and earth ground . This is not conclusive , if the neutral is bonded to earth ground . But try it , with various lites and / or other loads turned on .
I repeat , it sounds like a bad neutral . Could be at the " pole " which is feeding the barn or at the loadcenter that has the 2 P 50 amp CB ?
God bless
Wyr
#23
NEC does not require a main in the barn loadcenter .
#24
If i hold probes on screws i get 120v.