Found Odd Light Fixture Wiring...Question
Hello.
I am replacing an old two bulb ceiling light fixture. Upon removal of the old light I have found wiring that is unusual to me (a regular homeowner). I have described the wiring below:
LIGHT FIXTURE: there are two bulbs with white and black wires coming from each. The two whites are connected and the two blacks are connected.
JUNCTION BOX: there are two wires coming into the junction box, each with black, white and ground. One wire runs off somewhere and the other goes to a switch. Inside the box, the two white wires are connected, the two grounds are connected and the two black wires are loose.
CONNECTION: one of the black wires in the box went to the combined black wires for the two light bulbs and the other black wire in the box went to the combined white wires.
See pic below.

My question is whether this is correct. Why not white to white, black to black all around?
Thanks for your help.
Monomoy
I am replacing an old two bulb ceiling light fixture. Upon removal of the old light I have found wiring that is unusual to me (a regular homeowner). I have described the wiring below:
LIGHT FIXTURE: there are two bulbs with white and black wires coming from each. The two whites are connected and the two blacks are connected.
JUNCTION BOX: there are two wires coming into the junction box, each with black, white and ground. One wire runs off somewhere and the other goes to a switch. Inside the box, the two white wires are connected, the two grounds are connected and the two black wires are loose.
CONNECTION: one of the black wires in the box went to the combined black wires for the two light bulbs and the other black wire in the box went to the combined white wires.
See pic below.

My question is whether this is correct. Why not white to white, black to black all around?
Thanks for your help.
Monomoy
Last edited by Monomoy; 01-28-14 at 09:13 AM. Reason: upload pic
#2
there are two wires coming into the junction box, each with black, white and ground.
the other black wire in the box went to the combined white wires.
#3
My question is whether this is correct.
To correct this, the white wire going to the switch needs to be marked with electrical tape or permanent marker as Ray suggested and spliced to the black wire in the other cable. That will leave you with one black wire and one white wire, plus grounds, for connecting your fixture.
Why not white to white, black to black all around?
#4
Member
Thread Starter
Join Date: Jan 2014
Location: US
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Light
Yes, I have described it correctly. I just pulled another light in an adjoining room and it is done the same way, except that there are three cables entering that box. See pic below.

But, everything works through the switch?
NashKat1, you say that to correct this, "the white wire going to the switch needs to be marked with electrical tape or permanent marker as Ray suggested and spliced to the black wire in the other cable. That will leave you with one black wire and one white wire, plus grounds, for connecting your fixture."
So to restate this, the white wire from the switch should be spliced to the black wire from the other cable coming into the box. The white wire from the other cable is then no longer spliced to the other white wire and available to connect to the white wire on the fixture. I think I have this right. Yes?
The other light pictured above has 3 cables in the box and I would not know which of the other two cables to connect to from the switch....any ideas?
Thanks a lot.

But, everything works through the switch?
NashKat1, you say that to correct this, "the white wire going to the switch needs to be marked with electrical tape or permanent marker as Ray suggested and spliced to the black wire in the other cable. That will leave you with one black wire and one white wire, plus grounds, for connecting your fixture."
So to restate this, the white wire from the switch should be spliced to the black wire from the other cable coming into the box. The white wire from the other cable is then no longer spliced to the other white wire and available to connect to the white wire on the fixture. I think I have this right. Yes?
The other light pictured above has 3 cables in the box and I would not know which of the other two cables to connect to from the switch....any ideas?
Thanks a lot.
#5
Based on that picture it looks like you have several miswired switch loops along with the white appearing to be the hot.
#7
The other light pictured above has 3 cables in the box and I would not know which of the other two cables to connect to from the switch....any ideas?
Originally Posted by pcboss
Based on that picture it looks like you have... the white appearing to be the hot.
With the power off, you also need to pull the switch associated with the ceiling box with 3 cables in it and test for continuity to determine which of those cables is connected to the switch.
#9
the switch is on the neutral after the fixture. That means that turning the switch off does not kill power to the fixture.
#10
Be sure to label each wire before you disconnect things so you can put it back exactly the way it was (even though the finished result will not be what it was originally).
You will need to disconnect some wires in order to find out which cable supplies the power, which you need to find out.
You will need to disconnect some wires in order to find out which cable supplies the power, which you need to find out.
#11
Member
Thread Starter
Join Date: Jan 2014
Location: US
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks
Thanks - I see the issue now. Question for Ray2047 - in your picture, should the bottom wire in the switch loop say "ReColored Black"?....it is a white wire with black colored on the ends...yes? The other wire from the switch to the light is black.
Now, for the real novice questions:
how does one test wires for lead/power, continuity etc......sorry? Is there a sticky that covers this? I have a "Hi - Vis Voltage Tester" with red and black wires that power a small light. I also have a multimeter but never really figured out how to use it. I'm sure an internet search will yield lots but if there is a cut and paste or sticky thread that would be great. I'm new to this site. Thanks
Now, for the real novice questions:
how does one test wires for lead/power, continuity etc......sorry? Is there a sticky that covers this? I have a "Hi - Vis Voltage Tester" with red and black wires that power a small light. I also have a multimeter but never really figured out how to use it. I'm sure an internet search will yield lots but if there is a cut and paste or sticky thread that would be great. I'm new to this site. Thanks
Last edited by Monomoy; 01-29-14 at 08:33 AM. Reason: typo
#12
should the bottom wire in the switch loop say "ReColored Black"?