Adding 3 Gang Outlets + 1 for TV
#1
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Adding 3 Gang Outlets + 1 for TV
Hi there.
I just joined today because I am starting my first project in my new home.
In my living room I have two outlets, too far away for me to use with my entertainment center.
I do not want to have cables running outside my wall (extension/strips).
My project is to add a 3 duplex receptacles, 12" off the floor.
I will also like to run romex in the wall up to my mounted TV (6' up).
I've done some research and seems pretty basic to add a few outlets. My question is pertaining to the amount of connections I am adding.
I attached two images.
Would either of these plans work? Do I need anything special besides the back boxes (plastic), romex, receptacles and face plates?
I just joined today because I am starting my first project in my new home.
In my living room I have two outlets, too far away for me to use with my entertainment center.
I do not want to have cables running outside my wall (extension/strips).
My project is to add a 3 duplex receptacles, 12" off the floor.
I will also like to run romex in the wall up to my mounted TV (6' up).
I've done some research and seems pretty basic to add a few outlets. My question is pertaining to the amount of connections I am adding.
I attached two images.
Would either of these plans work? Do I need anything special besides the back boxes (plastic), romex, receptacles and face plates?
#3
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
It leads to another outlet.
There are two outlets. IN (left) and Out (right). I want to cut that romex connecting the two outlets and add the 3 duplexes.
EDIT:
I labeled IN/Out because that is how I've seen other diagrams. I take it as the IN side leads to the power source (panel) and OUT would lead to the next outlet.
I could be using these incorrectly, as I have no experience with electrical work (besides thermostats).
It seems fairly easy to add 1 outlet... but I don't know about 3, and then another splice to another outlet... then continuing down the line to the next preexisting outlet.
There are two outlets. IN (left) and Out (right). I want to cut that romex connecting the two outlets and add the 3 duplexes.
EDIT:
I labeled IN/Out because that is how I've seen other diagrams. I take it as the IN side leads to the power source (panel) and OUT would lead to the next outlet.
I could be using these incorrectly, as I have no experience with electrical work (besides thermostats).
It seems fairly easy to add 1 outlet... but I don't know about 3, and then another splice to another outlet... then continuing down the line to the next preexisting outlet.
Last edited by erew99; 01-28-14 at 01:45 PM. Reason: Explanation
#4
Your diagram is correct, however you may not have enough cable to ensure that you have at least 6" of free conductor from each cable.
#6
I just joined today
Would either of these plans work?
Splicing the feeds and pigtails together is generally preferable to using the devices to also make the circuit connections.
Do I need anything special besides the back boxes (plastic),
romex,
receptacles and face plates?
#7
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks I guess I'm just a little confused .
On the diagram:
Left side is in, feeding the new outlets. On the right is the out, going to another predxisting outlet.
For the outlet on top, I will run more nm-b cable to it. Ther will not be another out on that tv outlet.
Why wouldn't there be enough cable?
On the diagram:
Left side is in, feeding the new outlets. On the right is the out, going to another predxisting outlet.
For the outlet on top, I will run more nm-b cable to it. Ther will not be another out on that tv outlet.
Why wouldn't there be enough cable?
#9
Take a piece of cable 10' long. Now cut it in the middle giving you two 5' pieces. Try to install a box at the cut you need at least 6" more cable from both sides to allow the splice to be made in the box.
#12
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I will have my walls open (to studs) when doing this. So I can easily run new NM-B cable.
From what I gather, you cannot ground in a plastic box... so I do need to use a 3-gang metal for the outlets behind the entertainment center and then another 1-gang for behind the TV.
Is there a specific wirenut size I need to use for the all of this?
I am going to use something like this:
Shop STEEL CITY 44-1/4-cu in 3-Gang Old Work Metal Electrical Box at Lowes.com
Does this box allow the use of grounding screws?
From what I gather, you cannot ground in a plastic box... so I do need to use a 3-gang metal for the outlets behind the entertainment center and then another 1-gang for behind the TV.
Is there a specific wirenut size I need to use for the all of this?
I am going to use something like this:
Shop STEEL CITY 44-1/4-cu in 3-Gang Old Work Metal Electrical Box at Lowes.com
Does this box allow the use of grounding screws?
#13
There is no need to ground a plastic box. It s non-conductive.
I would use something like this.
Arlington | Home Theater • Audio/Video
A typical red wire nut is good for 5 #12's. More than that and you will need a large blue or gray.
I would use something like this.
Arlington | Home Theater • Audio/Video
A typical red wire nut is good for 5 #12's. More than that and you will need a large blue or gray.
#15
The receptacles do need to be grounded. A plastic box does not.
NM cable can be used with that box. You do need a proper connector.
NM cable can be used with that box. You do need a proper connector.
#16
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
So then why use a plastic box for outlets?
I'm not sure what components to use. The diagram should be good - what connects to what...
I will run new NM from existing outlet to the new outlet. Then another NM cable up to the TV.
That much is good.
So for this type of setup, I'd need to ground the duplex receptacles.
Does this require the use of a metal box to attach the ground wire to?
How would you ground all of those receptacles in the 3-gang box - whether it is metal or plastic?
I'm not sure what components to use. The diagram should be good - what connects to what...
I will run new NM from existing outlet to the new outlet. Then another NM cable up to the TV.
That much is good.
So for this type of setup, I'd need to ground the duplex receptacles.
Does this require the use of a metal box to attach the ground wire to?
How would you ground all of those receptacles in the 3-gang box - whether it is metal or plastic?
#17
Your diagrams show the proper receptacle grounding. Plastic is non-conductive so there is no point in connecting the ground to it.
Plastic boxes are typically cheaper and faster to work with and you save time be not needing to ground them.
Plastic boxes are typically cheaper and faster to work with and you save time be not needing to ground them.
#18
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Gotcha. So I'll use the plastic boxes then.
The grounds to the receptacles are all good.
For the ground wire specifically, can I use the same red wirenuts as I can w/ hot and neutral wires?
I'll probably go with the 2nd diagram (using the pigtails between receptacles).
This would require 3 red wire nuts. One for hot, one for neutral and one for ground.
The ground wire looks thicker/harder.
The grounds to the receptacles are all good.
For the ground wire specifically, can I use the same red wirenuts as I can w/ hot and neutral wires?
I'll probably go with the 2nd diagram (using the pigtails between receptacles).
This would require 3 red wire nuts. One for hot, one for neutral and one for ground.
The ground wire looks thicker/harder.
#19
You will need to see if the red wire nut is listed for the number of conductors you are trying to splice.
The ground wire is the same size in a 14-x or a 12-x cable.
The ground wire is the same size in a 14-x or a 12-x cable.
#22
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks. I appreciate all your help.
I'll go w/ diagram two and use the following behind the TV.
Arlington TVBU505BL-1 Recessed TV Outlet Box with Paintable Trim Plate, Black, 2-Gang - Amazon.com
I'll use plastic boxes and ground each receptacle using the ground wire in the NM-B cable.
I'll use the red nuts for the hot/neutral wires.
I'll use the large gray nut for the grounds.
Then test each receptacle using a meter prior to plugging any devices in.
Once everything looks good, I'll run my HDMI/Speakers/Coax/Subwoofer cables in the walls to new face plates behind the entertainment center.
I'll go w/ diagram two and use the following behind the TV.
Arlington TVBU505BL-1 Recessed TV Outlet Box with Paintable Trim Plate, Black, 2-Gang - Amazon.com
I'll use plastic boxes and ground each receptacle using the ground wire in the NM-B cable.
I'll use the red nuts for the hot/neutral wires.
I'll use the large gray nut for the grounds.
Then test each receptacle using a meter prior to plugging any devices in.
Once everything looks good, I'll run my HDMI/Speakers/Coax/Subwoofer cables in the walls to new face plates behind the entertainment center.
#23
I'll use plastic boxes and ground each receptacle using the ground wire in the NM-B cable.
I also connect each device to ground.
Then test each receptacle using a meter prior to plugging any devices in.
#25
How would you ground the box?
You can also install a ground tail, make one yourself, or use a wire nut with a pigtail built in.
#27
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I didn't realize more than one person had replied to my questions...
Thanks. I don't know what to do now... metal or plastic box...
For metal boxes (like the Arlington I linked) - I guess I have to ground the box itself. How can I do that and also ground the receptacles?
Thanks. I don't know what to do now... metal or plastic box...
For metal boxes (like the Arlington I linked) - I guess I have to ground the box itself. How can I do that and also ground the receptacles?
#28
If the ground is coming from the NM-B... and you attach that ground to the box/screw... the other end isn't available to use.
#29
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I'm specifically using Romex branded cable. So it has hot/neutral/ground all in the single cable.
For the images I posted. If using plastic boxes, would the diagram be correct?
For the images I posted. If using plastic boxes, would the diagram be correct?
#30
For the images I posted. If using plastic boxes, would the diagram be correct?
I'm specifically using Romex branded cable. So it has hot/neutral/ground all in the single cable
#31
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I'm just a bit confused on grounding the box.
If using plastic, then I don't need to ground the box. So the 2nd diagram will work.
No other question. I misunderstood the previous poster.
If using plastic, then I don't need to ground the box. So the 2nd diagram will work.
No other question. I misunderstood the previous poster.