Does a duplex receptacle count as a single or double outlet
#1
Member
Thread Starter
Join Date: Oct 2013
Location: Canada
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Does a duplex receptacle count as a single or double outlet
Does a duplex receptacle count as a single or double outlet. I am trying to determine the number of outlets on a single 15 amp circuit. I have found the following guidelines from the City of Winnipeg, Canada:
The maximum over-current device permitted for lights and receptacles is 15 amperes (fuse or circuit breaker) and a maximum of 12 outlets (lights and receptacles) may be connected to each 15 ampere branch circuit.
Additionally is it recommended to mix lights and receptacles on a single circuit - I am planning to take the power from a receptacle to feed a switch/light. Does code allow this and more importantly would an inspector approve it. I plan to do this in both bedrooms in my basement development.
Thanks all in advance.
The maximum over-current device permitted for lights and receptacles is 15 amperes (fuse or circuit breaker) and a maximum of 12 outlets (lights and receptacles) may be connected to each 15 ampere branch circuit.
Additionally is it recommended to mix lights and receptacles on a single circuit - I am planning to take the power from a receptacle to feed a switch/light. Does code allow this and more importantly would an inspector approve it. I plan to do this in both bedrooms in my basement development.
Thanks all in advance.
#2
Here, under the NEC, an outlet is the box where electricity may be tapped - let out. A duplex receptacle fits in one single gang device (outlet) box.
In addition, we consider it best practice to run 20A circuits for receptacles and separate 15A circuits for lighting. That way, a single fuse or circuit breaker can't put an entire room in the dark.
Can you post a link to the regulations you're looking at?
In addition, we consider it best practice to run 20A circuits for receptacles and separate 15A circuits for lighting. That way, a single fuse or circuit breaker can't put an entire room in the dark.
Can you post a link to the regulations you're looking at?
#3
Member
Thread Starter
Join Date: Oct 2013
Location: Canada
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
#5
Thank you for the link. My eyes started to glaze over and I started to lose focus after I read these two requirements:
It makes no sense to talk about 20A receptacles on 15A circuits. It makes even less sense, with today's loads, to limit all circuits to 15A.
Then I got to this part and hung it up:
No, I'm not interested in paying for 20A T-slot receptacles to install on a 15A circuit. And the kitchen countertop receptacle circuits are limited to 15A? Good luck with that. One good-sized microwave or toaster oven will blow one of those all bu itself.
We have one or two Canadian electricians here. Maybe one of them will stop by and help us Yankees understand this.
2. All 15 amp and 20 amp receptacles must be the tamper-resistant
type unless they are dedicated for microwaves, refrigerators,
freezers or kitchen counters or located in attics or crawlspaces.
...
4. The maximum over-current device permitted for lights
and receptacles is 15 amperes (fuse or circuit breaker) and
a maximum of 12 outlets (lights and receptacles) may be
connected to each 15 ampere branch circuit.
type unless they are dedicated for microwaves, refrigerators,
freezers or kitchen counters or located in attics or crawlspaces.
...
4. The maximum over-current device permitted for lights
and receptacles is 15 amperes (fuse or circuit breaker) and
a maximum of 12 outlets (lights and receptacles) may be
connected to each 15 ampere branch circuit.
Then I got to this part and hung it up:
d) Kitchen counter receptacles must be of the “15A split” type, as illustrated in FIGURE 20 on page 26, or 20A T-slot.
We have one or two Canadian electricians here. Maybe one of them will stop by and help us Yankees understand this.
#6
Member
The CEC limits lighting to a 15a circuit. The way I read it is that if you put lighting AND receptacles on one circuit, you are limited to 15a. If you have a receptacle ONLY circuit, you can use 12ga on a 20a circuit or 14ga on a 15a circuit. A 20a circuit must have T-slot receptacles.
Kitchen countertop circuits can be either 20a (with T-slot) or you can use a 15a split receptacle. I think given the GFCI requirements, any new work would be with a 20a circuit.
Kitchen countertop circuits can be either 20a (with T-slot) or you can use a 15a split receptacle. I think given the GFCI requirements, any new work would be with a 20a circuit.
#7
The CEC limits lighting to a 15a circuit. The way I read it is that if you put lighting AND receptacles on one circuit, you are limited to 15a. If you have a receptacle ONLY circuit, you can use 12ga on a 20a circuit or 14ga on a 15a circuit. A 20a circuit must have T-slot receptacles.
Kitchen countertop circuits can be either 20a (with T-slot) or you can use a 15a split receptacle. I think given the GFCI requirements, any new work would be with a 20a circuit.
Kitchen countertop circuits can be either 20a (with T-slot) or you can use a 15a split receptacle. I think given the GFCI requirements, any new work would be with a 20a circuit.

#8
wpsteel,
According to the definitions in the CEC...
"Receptacle - one or more female contact devices, on the same yoke, installed at an outlet for the connection of one or more attachment plugs."
So yes a duplex receptacle counts as one receptacle, not two.
Also, the rule of 12 outlets on a 15A circuit comes from the rule that you can only load your breaker to 80%. Each receptacle and light is considered 1A UNLESS the load is known. For example an LED fixture known to only pull .5A will be taken as .5A instead of 1A. Receptacles can accept a variety of devices though so are always considered 1A.
And mixing lighting and receptacles is optional. I prefer not to. Find a mixed circuit in your home and try turning on the vacuum with the lights on...
Nash,
Honestly, that document makes more sense than trying to read and interpret the codebook.
- Yes every receptacle, including GFCI, must be tamper resistant unless inaccessible (ie: the fridge and microwave dedicated receptacles) OR if it is 2M above the floor.
- As fins said, you can have 20A receptacle circuits on 12AWG wire with appropriate receptacles.
- Kitchen receptacles give you options. You may put no more than two receptacles per circuit, and they can be 15A split, or 20A.
- The lighting limit is 15A in residential only. Commercial lighting circuits can be 15A or 20A.
According to the definitions in the CEC...
"Receptacle - one or more female contact devices, on the same yoke, installed at an outlet for the connection of one or more attachment plugs."
So yes a duplex receptacle counts as one receptacle, not two.
Also, the rule of 12 outlets on a 15A circuit comes from the rule that you can only load your breaker to 80%. Each receptacle and light is considered 1A UNLESS the load is known. For example an LED fixture known to only pull .5A will be taken as .5A instead of 1A. Receptacles can accept a variety of devices though so are always considered 1A.
And mixing lighting and receptacles is optional. I prefer not to. Find a mixed circuit in your home and try turning on the vacuum with the lights on...
Nash,
Honestly, that document makes more sense than trying to read and interpret the codebook.
- Yes every receptacle, including GFCI, must be tamper resistant unless inaccessible (ie: the fridge and microwave dedicated receptacles) OR if it is 2M above the floor.
- As fins said, you can have 20A receptacle circuits on 12AWG wire with appropriate receptacles.
- Kitchen receptacles give you options. You may put no more than two receptacles per circuit, and they can be 15A split, or 20A.
- The lighting limit is 15A in residential only. Commercial lighting circuits can be 15A or 20A.
#10
Their wording is dumb Joe, they mention 20A receptacles, and "lights and receptacles". Residential lighting circuits are limited to 15A so if you mix "lights and receptacles" you are limited to 15A on that circuit.
However a strictly 20A receptacle circuit is ok.
However a strictly 20A receptacle circuit is ok.
#11
However a strictly 20A receptacle circuit is ok.
#12
I think that is an oversight in their documentation. If they didn't allow 20A circuits I would think they would axe any mention to 20A devices.