Damaged NM cable?
I have a LONG run of 10/3 with ground NM cable running from panel to electric dryer.
I found a small portion of the outter cable damaged, when I pulled back the sheath, one of the conductors is also damaged/nicked/burned.
Do I need to replace entire run, or can a junction box be installed?
I found a small portion of the outter cable damaged, when I pulled back the sheath, one of the conductors is also damaged/nicked/burned.
Do I need to replace entire run, or can a junction box be installed?
#4
Member
Thread Starter
Join Date: Nov 2013
Posts: 269
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Its directly center between two ceiling joists. I would have enough slack perhaps if I can mount a box in the center of the two joists.
I need an idea of both a one box method and a two box method... the slack would be an issue if I mount a single box in the center of the joists?
I also noticed this is 8/3 (on a 30A breaker)... overkill, but is that an issue?
I need an idea of both a one box method and a two box method... the slack would be an issue if I mount a single box in the center of the joists?
I also noticed this is 8/3 (on a 30A breaker)... overkill, but is that an issue?
Last edited by rards; 02-03-14 at 07:36 AM.
#5
Its directly center between two ceiling joists
#7
I would have enough slack perhaps if I can mount a box in the center of the two joists.
Should I pretwist them or so something otherwise different than I would with 12or14?

#8
Member
Thread Starter
Join Date: Nov 2013
Posts: 269
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Why the funny confused face nashkat?
Was wondering if something like a terminal block or split bolt is necessary....plus this is stranded big stuff and I wasn't sure if they pretwist correctly?
Was wondering if something like a terminal block or split bolt is necessary....plus this is stranded big stuff and I wasn't sure if they pretwist correctly?
#9
Why the funny confused face nashkat?
Should I pretwist them or so something otherwise different than I would with 12or14?
Was wondering if something like a terminal block or split bolt is necessary....
plus this is stranded big stuff and I wasn't sure if they pretwist correctly?
To answer your question, many folks like to tighten the twist in stranded conductors and then twist them together the same way they would if they were solid conductors. I've found though - and this is just my own experience - that I get a better connection in the splice if I untwist the conductors so they look like brushes and then twist those two brushes together. The brushes will usually interweave and mesh into each other when it's done that way, IMX.
#10
No, no split bolts or other special connectors needed. Wire nuts are okay. If the box(es) are metal you do need to pigtail the ground to the box. Not sure of pigtail size. Pros can answer that one.
#11
Member
Thread Starter
Join Date: Nov 2013
Posts: 269
Upvotes: 0
Received 0 Upvotes
on
0 Posts
As for the grounds Ray its NM so if I use metal box(es) I would just splice the grounds in the box as well (2 wires in and out)? Im taking it as your saying I need a 3rd wire pigtail to box too?
#13
Member
Thread Starter
Join Date: Nov 2013
Posts: 269
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I would imagine this type of damage was done during installation, judging by the date on the cable back in 2002. And judging from the burn, I would think the breaker would have tripped at that point. But Im wondering why the breaker never tripped when using the dryer all this time?
The red conductor has a nick in the insulation and there is scortching. But it doesn't look like the other wires insulation was damaged and there is still paper I think on the ground. So where does the scortch come from?
If I didn't happen upon it and see the damage, how would have likely been discovered? Do you think the damage wire would have burned thru the paper and shorted to ground or would that wire just failed and I would only be getting 120 at the dryer? Or worse, a fire? I was actually touching the energized bare spot before I realized what it was....
p.s.- I had a raco bracket on hand but it isn't the kind that has a threaded connector to go thru the center knockout.... it has a screw and a little u shaped washer and I am having a hard time figuring out if that works with a 4x4 box.
. If I go the route of mounting a box in the center of the joists, would a 2x4 screws driven at angle to hold it in place be sufficient?
The red conductor has a nick in the insulation and there is scortching. But it doesn't look like the other wires insulation was damaged and there is still paper I think on the ground. So where does the scortch come from?
If I didn't happen upon it and see the damage, how would have likely been discovered? Do you think the damage wire would have burned thru the paper and shorted to ground or would that wire just failed and I would only be getting 120 at the dryer? Or worse, a fire? I was actually touching the energized bare spot before I realized what it was....
p.s.- I had a raco bracket on hand but it isn't the kind that has a threaded connector to go thru the center knockout.... it has a screw and a little u shaped washer and I am having a hard time figuring out if that works with a 4x4 box.
. If I go the route of mounting a box in the center of the joists, would a 2x4 screws driven at angle to hold it in place be sufficient?
#15
judging from the burn, I would think the breaker would have tripped at that point. But Im wondering why the breaker never tripped when using the dryer all this time?
The red conductor has a nick in the insulation and there is scortching. But it doesn't look like the other wires insulation was damaged and there is still paper I think on the ground. So where does the scortch come from?
If I didn't happen upon it and see the damage, how would have likely been discovered? Do you think the damage wire would have burned thru the paper and shorted to ground or would that wire just failed and I would only be getting 120 at the dryer? Or worse, a fire?
I had a raco bracket on hand but it isn't the kind that has a threaded connector to go thru the center knockout.... it has a screw and a little u shaped washer and I am having a hard time figuring out if that works with a 4x4 box.
If I go the route of mounting a box in the center of the joists, would a 2x4 screws driven at angle to hold it in place be sufficient?
How are you planning to get 8" of each cable end inside the box if you don't mount a second box?
#16
Member
Thread Starter
Join Date: Nov 2013
Posts: 269
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Its just like this one but doesn't have the male threaded piece you see in the photo (which I assume goes thru the top 1/2" knockout)... just the washer and like a pan head screw. The screw fits thru a hole in the box but I am not sure if that's the proper way to mount it.

I can get 4 maybe 6 inches I think of slack in the box, working with some scrap #8 and I am realizing I will need more than that... this stuff is very hard for me to work with. The 2 box route looks to be the way to go but now I gotta sweat making 4 big joints.
Just to confirm, I will need to bring 8/3NM thru the 3/4" knockouts with 3/4" connectors.

How are you planning to get 8" of each cable end inside the box if you don't mount a second box?
Just to confirm, I will need to bring 8/3NM thru the 3/4" knockouts with 3/4" connectors.
#17
Its similar to this but the one I have doesn't have the male threaded piece... just the washer and like a pan head screw. The screw fits thru a hole in the box but I am not sure if that's the proper way to mount it.
I can get 4 maybe 6 inches I think of slack in the box, working with some scrap #8 and I am realizing I will need more than that...
If I were doing this, I'd be thinking about mounting a box in the joist bay on each side of the damage and pulling the cable ends back to there to splice them to a repair piece.
this stuff is very hard for me to work with.
The 2 box route looks to be the way to go but now I gotta sweat making 4 big joints.
#19
Member
Thread Starter
Join Date: Nov 2013
Posts: 269
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Another option I have is replace about 20' from panel to damage. Its about 30' ft in the other direction.
Obviously more costly but is that a significantly better idea than the two box idea?
How would a service electrician do it if called to the house?
I know its OK to overfuse in this situation but another thing I was thinking. Are 30A breakers designed to use #8? I have 1" GE brand breakers.
Another confusion... 8/3 with ground used with a 30A dryer plug... I didn't take it apart to check but what is the white wire used for then? Or is that the third prong and the bare ground just grounds the box?
Obviously more costly but is that a significantly better idea than the two box idea?
How would a service electrician do it if called to the house?
8-3 is fine on a 30 amp breaker.
Another confusion... 8/3 with ground used with a 30A dryer plug... I didn't take it apart to check but what is the white wire used for then? Or is that the third prong and the bare ground just grounds the box?
Last edited by rards; 02-03-14 at 03:07 PM.
#20
Are 30A breakers designed to use #8?
8/3 with ground used with a 30A dryer plug... what is the white wire used for
Last edited by ray2047; 02-03-14 at 05:33 PM.
#21
Member
Thread Starter
Join Date: Nov 2013
Posts: 269
Upvotes: 0
Received 0 Upvotes
on
0 Posts
How are you planning to get 8" of each cable end inside the box
#22
why 8" as opposed to the standard 6"?
#23
The code requires 6" minimum of free conductor in the box from each cable. You are probably going to need 2 boxes or to run a new portion of the run.
To splice just line up the ends of the wires and add the splice cap.
To splice just line up the ends of the wires and add the splice cap.
#24
Member
Thread Starter
Join Date: Nov 2013
Posts: 269
Upvotes: 0
Received 0 Upvotes
on
0 Posts
You are probably going to need 2 boxes or to run a new portion of the run.
To splice just line up the ends of the wires and add the splice cap.
I was experimenting with Nashkats brush technique and it seems to work but I have never worked with nor have seen what a properly twisted large wire splice like this should look like.....
#25
Member
Thread Starter
Join Date: Nov 2013
Posts: 269
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Got it done this morning. Went smooth. I was able to undo the rest of the cable and create enough slack to mount a single box on one of the joists. I then had at least 6-8" of wire to work with. I used a 4x4x2 1/8 box with the stud bracket on the side and mounted it to the joist. I used the 1/2" knockouts and appropriate cable clamps.
I was getting 120 from each hot to the neutral and 120 from each hot to the ground and 240 between the hots. I connected the ground with a pigtail to the box as instructed and used large Gardner and Bender Blue wire nuts.
Hopefully I didn't loosen the device on the other end with my pulling and tugging.... but it appears to be functional now.
I was getting 120 from each hot to the neutral and 120 from each hot to the ground and 240 between the hots. I connected the ground with a pigtail to the box as instructed and used large Gardner and Bender Blue wire nuts.
Hopefully I didn't loosen the device on the other end with my pulling and tugging.... but it appears to be functional now.
#27
Glad you got it done, and thanks for the update.
??? All cables should be secured within 8" of any box that they enter. That's required in order to prevent their being pulled loose from a connection inside the box. Is your cable secured there?
Hopefully I didn't loosen the device on the other end with my pulling and tugging.... but it appears to be functional now.
#28
Member
Thread Starter
Join Date: Nov 2013
Posts: 269
Upvotes: 0
Received 0 Upvotes
on
0 Posts
??? All cables should be secured within 8" of any box that they enter. That's required in order to prevent their being pulled loose from a connection inside the box. Is your cable secured there?
Pulling the old staple bent them to much for reuse so I used some new plastic Gardner and Bender straps to resecure the cable when I was done.
#29
OK, I'll hope along with you that you didn't mess up anything inside a box while you were working. It sounds like you left the cable secured to the box the whole time. If you can't see that it ever moved relative to the clamp at the box it's probably fine.
#30
Member
Thread Starter
Join Date: Nov 2013
Posts: 269
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Nashkat1
OK, I'll hope along with you that you didn't mess up anything inside a box while you were working. It sounds like you left the cable secured to the box the whole time. If you can't see that it ever moved relative to the clamp at the box it's probably fine.
OK, I'll hope along with you that you didn't mess up anything inside a box while you were working. It sounds like you left the cable secured to the box the whole time. If you can't see that it ever moved relative to the clamp at the box it's probably fine.
Save your hope for the lottery Nashkat... again, I used a few temporary staples to secure it while working.....so I should be good to go.
Thanks for the help too Ray, I would have missed the pigtailing grounds if it wasn't for you mentioning it.