Dimmer/outlet question


  #1  
Old 02-09-14, 09:05 PM
J
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
Dimmer/outlet question

Can I use a standard dimmer switch for a switch that controls one ceiling light fixture and half of an outlet?
 
  #2  
Old 02-09-14, 09:14 PM
B
Member
Join Date: Oct 2013
Location: United States
Posts: 189
Upvotes: 0
Received 0 Upvotes on 0 Posts
Dimmer question

Can I use a standard dimmer switch for a switch that controls one ceiling light fixture
Yes

and half of an outlet?
NO. The NEC does not allow receptacles to be controlled by a lighting dimmer. Items plugged into that outlet could be damaged (motors, computers, TV's etc).
 
  #3  
Old 02-09-14, 09:30 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
and half of an outlet?
Only if it is a dimmer receptacle and you change the plug on lamp to fit a dimmer receptacle.

Name:  120770716.jpg
Views: 1013
Size:  6.5 KB Name:  WH-250-05.jpg
Views: 540
Size:  15.8 KB

Buy Scr-20-Hfdu-Tp - Lutron - 20A Satin Color Dimmer Receptacle Taupe From Westway Electric Supply
https://www.mrsupply.com/lutron-repl...fdu-10-wh.html
 
  #4  
Old 02-09-14, 09:56 PM
B
Member
Join Date: Oct 2013
Location: United States
Posts: 189
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ray,I like that. Never seen those with the blocking feature. Somebody had a great idea. Was wondering why the NEC changed and said the dimmer was for permanent light fixtures "Unless listed for the control of other loads" I wonder if dimmers include listing with that receptacle, I would assume so if Lutron's got it on the market. Good Call!
 
 