I have a receptacle in a closet that I really have no use for. This is directly adjacent to the access for my attic, which I have no light in. Can I remove the receptacle and use the wiring to wire in a pull chain light fixture in my attic? Also the few pull chain lights I did browse were rated at 250V, as in heavy appliance power? Didn't understand that.
 
  #2  
Old 02-15-14, 03:47 AM
J
Banned. Rule And/Or Policy Violation
Join Date: Apr 2013
Location: USA
Posts: 3,860
Upvotes: 0
Received 1 Upvote on 1 Post
No need to remove the whole thing, box and all. Just use the box as a junction box and add a blank cover over the old receptacle.
250V is the max voltage it's rated for. It will work fine on a 120 volt circuit.
Do not just have the wire hanging in the air from the top plate to the place your going to add the light.
You will need to add a 2 X 4 to attach the wiring to with wire staples.
 
  #3  
Old 02-15-14, 07:14 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
You will need an octagon box and what is known as a keyed lamp holder by old time electricians. They only cost a couple of bucks.

Name:  HES_110.jpg
Views: 176
Size:  3.4 KB

Name:  lev9816c.jpg
Views: 138
Size:  11.2 KB
Lamp Holder Fixture - AZ Partsmaster

Can I remove the receptacle and use the wiring to wire in a pull chain light fixture in my attic? Also the few pull chain lights
Usually the cable is stapled to the stud so it can't be pulled up. However if you can find where it comes through the top plate you can cut it there leaving yourself some extra to work with, fasten a switch box or hexagon box to the top plate* and run new cable to the light. 12-2 NM-b if 20 amp breaker or 14-2 if 15 amp breaker.

the few pull chain lights I did browse were rated at 250V, as in heavy appliance power?
That was the maximum voltage rating for the fixture not the voltage it operates at.

* If there are two cables in the receptacle box they will have to be spliced together in the new attic junction box. You could also keep the existing receptacle "hot" but that would probably require two junction boxes.
 

Last edited by ray2047; 02-15-14 at 09:32 AM.
  #4  
Old 02-15-14, 08:22 AM
S
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 10
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yup thats it! Thanks for the help.
 
  #5  
Old 02-19-14, 12:15 AM
S
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 10
Upvotes: 0
Received 0 Upvotes on 0 Posts
Just wanted to clarify something Ray, the box shown is for my cable splice right? I'll need a round ceiling box for the light fixture as well, correct?
 
  #6  
Old 02-19-14, 03:07 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,935
Received 181 Upvotes on 159 Posts
The box shown will be for the light. The splice will originate where the receptacle is.
 
  #7  
Old 02-19-14, 04:24 AM
S
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 10
Upvotes: 0
Received 0 Upvotes on 0 Posts
Maybe I should clarify. The receptacle is, if this is the correct terminology, at the end of the circuit. There are only 2 wires on it. I was wanting to just disconnect and remove the receptacle, then use that cable in the attic to power the new light. Because of the location of the old cable I thought I would trim the existing cable from the old receptacle, add a new jbox, then run new cable from that jbox to wherever I mount the light. That's where I got two boxes.
 
  #8  
Old 02-19-14, 06:54 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
I was wanting to just disconnect and remove the receptacle, then use that cable in the attic to power the new light. Because of the location of the old cable I thought I would trim the existing cable from the old receptacle, add a new jbox, then run new cable from that jbox to wherever I mount the light.
And as I previously replied:
Usually the cable is stapled to the stud so it can't be pulled up. However if you can find where it comes through the top plate you can cut it there leaving yourself some extra to work with, fasten a switch box or hexagon box to the top plate and run new cable to the light. 12-2 NM-b if 20 amp breaker or 14-2 if 15 amp breaker.
So you can use octagon boxes in both places*. The splice box would have a blank cover. Assuming the cable to the receptacle contains a ground wire (ungrounded circuits can't be extended) if metal boxes are used the grounds are tied together and pigtailed to each box.

*A switch box could be used for the splice box in the attic but octagons are more traditional in attics and have more room for connections. Octagons are used for the light fixture.
 
  #9  
Old 02-19-14, 06:12 PM
S
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 10
Upvotes: 0
Received 0 Upvotes on 0 Posts
The splice will originate where the receptacle is.
Gotcha. This through me off for a sec. Thanks again.
 
 

Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: