Changing receptacle location and use
I have a receptacle in a closet that I really have no use for. This is directly adjacent to the access for my attic, which I have no light in. Can I remove the receptacle and use the wiring to wire in a pull chain light fixture in my attic? Also the few pull chain lights I did browse were rated at 250V, as in heavy appliance power? Didn't understand that.
#2
No need to remove the whole thing, box and all. Just use the box as a junction box and add a blank cover over the old receptacle.
250V is the max voltage it's rated for. It will work fine on a 120 volt circuit.
Do not just have the wire hanging in the air from the top plate to the place your going to add the light.
You will need to add a 2 X 4 to attach the wiring to with wire staples.
250V is the max voltage it's rated for. It will work fine on a 120 volt circuit.
Do not just have the wire hanging in the air from the top plate to the place your going to add the light.
You will need to add a 2 X 4 to attach the wiring to with wire staples.
#3
You will need an octagon box and what is known as a keyed lamp holder by old time electricians. They only cost a couple of bucks.


Lamp Holder Fixture - AZ Partsmaster
Usually the cable is stapled to the stud so it can't be pulled up. However if you can find where it comes through the top plate you can cut it there leaving yourself some extra to work with, fasten a switch box or hexagon box to the top plate* and run new cable to the light. 12-2 NM-b if 20 amp breaker or 14-2 if 15 amp breaker.
That was the maximum voltage rating for the fixture not the voltage it operates at.
* If there are two cables in the receptacle box they will have to be spliced together in the new attic junction box. You could also keep the existing receptacle "hot" but that would probably require two junction boxes.


Lamp Holder Fixture - AZ Partsmaster
Can I remove the receptacle and use the wiring to wire in a pull chain light fixture in my attic? Also the few pull chain lights
the few pull chain lights I did browse were rated at 250V, as in heavy appliance power?
* If there are two cables in the receptacle box they will have to be spliced together in the new attic junction box. You could also keep the existing receptacle "hot" but that would probably require two junction boxes.
Last edited by ray2047; 02-15-14 at 09:32 AM.
#7
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 10
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Maybe I should clarify. The receptacle is, if this is the correct terminology, at the end of the circuit. There are only 2 wires on it. I was wanting to just disconnect and remove the receptacle, then use that cable in the attic to power the new light. Because of the location of the old cable I thought I would trim the existing cable from the old receptacle, add a new jbox, then run new cable from that jbox to wherever I mount the light. That's where I got two boxes.
#8
I was wanting to just disconnect and remove the receptacle, then use that cable in the attic to power the new light. Because of the location of the old cable I thought I would trim the existing cable from the old receptacle, add a new jbox, then run new cable from that jbox to wherever I mount the light.
Usually the cable is stapled to the stud so it can't be pulled up. However if you can find where it comes through the top plate you can cut it there leaving yourself some extra to work with, fasten a switch box or hexagon box to the top plate and run new cable to the light. 12-2 NM-b if 20 amp breaker or 14-2 if 15 amp breaker.
*A switch box could be used for the splice box in the attic but octagons are more traditional in attics and have more room for connections. Octagons are used for the light fixture.