Using a 3 pole circuit breaker with 2 wires

I have an enclosure with a 3 pole breaker but my house only has 2 hot wires, can I use the circuit breaker safely without any harm?
 
Sponsored Links
  #2  
Old 02-20-14, 07:05 AM
Member
Join Date: Mar 2010
Location: USA
Posts: 3,757
Received 42 Votes on 40 Posts
It will work well using the 3 pole (triple wide triple) breaker for a 2 hot plus neutral 120/240 volt circuit or even a one hot plus neutral 120 volt circuit.

Most likely the enclosure was or is for a 3 phase electrical system but you can use the phases individually (provided you have a neutral) or two at a time (for 240 or 208 volts depending on the system).

The disadvantage of using one 3 pole breaker instead of 3 single pole breakers is that if one circuit should trip its breaker, up to 2 other circuits (sharing the breaker set) will be flipped off too.

Be sure you have a neutral in the box before connecting up a 120 volt circuit. You may not use ground in lieu of neutral. Also measure the voltage between the chosen breaker terminal and neutral before connecting it up. In some 3 phase systems (240 volt delta) one pole will measure 208 volts to neutral and you never want to use that pole all by itself.
 
  #3  
Old 02-20-14, 07:19 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,290
Received 43 Votes on 35 Posts
I have an enclosure with a 3 pole breaker but my house only has 2 hot wires, can I use the circuit breaker safely without any harm?
Where are you wanting to use the 3 pole breaker, will this be your main service disconnect? Does the enclosure have a neutral bar?
 
  #4  
Old 02-20-14, 08:37 AM
Member
Thread Starter
Join Date: Oct 2008
Location: NYC
Posts: 433
Received 0 Votes on 0 Posts
Yes, I want to use it as a main service disconnect. Yes there is a neutral bar.
 
  #5  
Old 02-20-14, 09:17 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,997
Received 40 Votes on 35 Posts
Using a 3 phase panel will also have 1/3 of the panel spaces dead.
 
  #6  
Old 02-20-14, 09:33 AM
Member
Thread Starter
Join Date: Oct 2008
Location: NYC
Posts: 433
Received 0 Votes on 0 Posts
I forgot to ask in my last post, when connecting, should I connect the neutral first?
 
  #7  
Old 02-20-14, 09:44 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,997
Received 40 Votes on 35 Posts
All work should be done with the panel off.

Many like to cut-in a panel doing grounds first, neutrals and then the hots out of practice.
 
  #8  
Old 02-20-14, 06:58 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,290
Received 43 Votes on 35 Posts
Yes, I want to use it as a main service disconnect. Yes there is a neutral bar.
Is it service entrance rated? It needs to be.

zizanio
I forgot to ask in my last post, when connecting, should I connect the neutral first?
It shouldn't make any difference because the meter should be pulled or the service disconnected by the power company and everything should be dead.
 
  #9  
Old 02-21-14, 12:03 PM
Member
Thread Starter
Join Date: Oct 2008
Location: NYC
Posts: 433
Received 0 Votes on 0 Posts
Thank you everyone for your help. One last question. Is there a distance limit from the service entrance? Does it have to be within 5 feet or 10 feet?
 
  #10  
Old 02-21-14, 12:26 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,997
Received 40 Votes on 35 Posts
The NEC requires the unfused conductors to be "as short as practical". No actual distance is specified. This is up to the inspector.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: