Just wanted to check before doing something stupid with my multimeter.
To check incoming power from the main service in my panel.
I would touch one probe to the neutral screw on the neutral lug. And the other probe then to the screw on one hot leg. 120.
Then repeat the process on the other leg for 120. Or one probe on the screw to one leg to the other screw on the other leg 240
The same idea would be used to check the main breaker using the breaker screws and the main lug screw on the neutral?
Also how do I check the mains hot to ground. and neutral to ground? (or is neutral to ground the same thing in the main panel?)
Thanks,
Thanks,
As long as the meter is set for the correct voltage range and has the correct safety rating your process is correct.
Neutral to ground should be zero in the service panel.
Checking hot leg to neutral is checking ground right? Or do I check hot leg to the metal enclosure since the two are bonded?
And if I was tightening a circuit breakers screws, or replacing one, is it best to turn off the breaker and then tighten when its still attached to the busbar or should I be torqueing with the breaker in my hand?
And if tightening screws on the neutral bus, why is it alright to do so with the power on? Or should I turn off the main?
It is always safer to work with the power off in the panel.
I would tighten the screws with the breaker turned off, but installed.