Requirements for AC Disconnect

I need to install a new disconnect for my residential AC condenser unit. I'm installing a 30A fusible pullout disconnect. The old disconnect is located behind the unit, which I don't believe is legal.

My understanding is that I need 36" clearance in the front and 30" side clearance (15" on each side). Is this correct? Also, is an outlet required for servicing the unit?
 
Sponsored Links
  #2  
Old 02-21-14, 04:41 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,066
I'm installing a 30A fusible pullout disconnect.
Normally residential units have built in protection and unfused disconnects are used.
My understanding is that I need 36" clearance in the front and 30" side clearance (15" on each side). Is this correct?
That applies to service panels, not disconnects.
Also, is an outlet required for servicing the unit?
Usually. Check with your AHJ.
 
  #3  
Old 02-21-14, 04:45 PM
Member
Thread Starter
Join Date: Apr 2009
Location: Ohio
Posts: 54
I'm using a fused disconnect because the new unit has a max fuse size of 25A, So I'm fusing down my 30A circuit.
 
  #4  
Old 02-21-14, 06:14 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,405
You could also change the breaker to 25 amps. That being said, if the label says fused disconnect, some inspectors will insist on fused protection like you are planning.
 
  #5  
Old 02-21-14, 09:50 PM
Member
Thread Starter
Join Date: Apr 2009
Location: Ohio
Posts: 54
So anyone know what the clearance requirements are?
 
  #6  
Old 02-22-14, 12:27 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,595
I would go with the 30x 36. The unit does not need to be centered.
 
  #7  
Old 02-22-14, 09:13 AM
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 2,117
NEC Art. 210.63 requires a receptacle outlet for the servicing of heating , A.C., and refrigeration equiptments , but that's , as regards your situation, a "new installation" requirement, but it would be in your best interest to provide such receptacle.
 