Wire is hot, but no light at outlet
Old 02-23-14, 01:56 PM
D
I have switch that turns on 5 kitchen lights. The lights stopped working yesterday. I assumed it was the switch and just went ahead and replaced it, but that did not work.
I got a non-contact voltage tester. The switch is hot, when turned on. I pulled out a bulb and the tester says the outlet is hot as well.
I checked the wire in the outlet that goes to ground to make sure it was not corroded, and it looks fine.
Any suggestions on what I should check next?
Old 02-23-14, 02:57 PM
ray2047's Avatar
Useless for this purpose. Your money would have been better spent on a cheap ($8-$15) analog multimeter.
A circuit will work fine with out a ground. It is for safety not function.
Tell us all the wires in the switch and how they are connected.
Old 02-23-14, 04:08 PM
D
Sorry I was incorrect, I did not check the ground. Thats the negative one I guess..or the one that goes back..not sure what its called
Ok so:
- Switch is not grounded
- One wire comes in goes into a cap, cap is attached to switch via another wire.
- Second wire, does the same, goes into the other end of the switch.
I checked under both the caps and the cables look fine.
What would I test with a multimeter?
Old 02-23-14, 04:44 PM
ray2047's Avatar
Odd if I understand you correctly or do you mean you have a dimmer with two leads? If there are only two wires in the box, a black and white, and they are connected to the switch turn off the breaker and connect the two house wires together with a wire nut. Turn the breaker on and check to see if the lights work.
Old 02-23-14, 04:50 PM
D
Only two wires. Already flipped the breaker..no dice. Guess I'll call for professional help, I'm already way beyond my abilities here.
Old 02-25-14, 03:54 PM
D
Just updating this post with the answer.
Essentially the problem was that one of the neutral wires got loose.
Neutral from the switch (this was working fine) was going to a chandelier. Same neutral from the chandelier goes to the kitchen can lights.
The one inside the chandelier was loose...my kid threw his ball at it.