On a 200amp service entry panel----would the main breaker be two ganged 100amps, or one 200amp main breaker?

In other words, how much does each leg of the 240vac (120v---neutral---120v) deliver? If the total is 200amps, then it seems each leg would be 100amps.
 
  #2  
Old 02-27-14, 02:10 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,980
Received 196 Upvotes on 172 Posts
Each leg will allow up to 200 amps to flow. It is not 100 per leg on a 200 amp service.
 
  #3  
Old 02-27-14, 06:15 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
(120v---neutral---120v)
That is wrong. It is 240----neutral----240. Each pole of the main breaker has 240 volts on it.