abandoning 3 circuits - removing wires?
#1
Member
Thread Starter
Join Date: Oct 2013
Posts: 487
Upvotes: 0
Received 0 Upvotes
on
0 Posts
abandoning 3 circuits - removing wires?
Someone wired up 3 useless circuits.
All three in one 1/2" conduit. 5 #14's.
circuit A and B are a multiwire branch circuit (each only controls 1 outlet!!?)
circuit C (controls 3 can lights and 2 outlets).
I need the space in my panel. I would like to completely remove the multiwire circuits. I would like to remove the wires from the panel and conduit....
can I safely pull 3 of the 5 wires out of the pipe or are they likely tangled? And how do I know I am yanking the correct neutral wire?
All three in one 1/2" conduit. 5 #14's.
circuit A and B are a multiwire branch circuit (each only controls 1 outlet!!?)
circuit C (controls 3 can lights and 2 outlets).
I need the space in my panel. I would like to completely remove the multiwire circuits. I would like to remove the wires from the panel and conduit....
can I safely pull 3 of the 5 wires out of the pipe or are they likely tangled? And how do I know I am yanking the correct neutral wire?
#2
I would like to completely remove the multiwire circuits. I would like to remove the wires from the panel and conduit....
can I safely pull 3 of the 5 wires out of the pipe or are they likely tangled?
can I safely pull 3 of the 5 wires out of the pipe or are they likely tangled?
And how do I know I am yanking the correct neutral wire?
#3
Member
Thread Starter
Join Date: Oct 2013
Posts: 487
Upvotes: 0
Received 0 Upvotes
on
0 Posts
More hackery... all three had to come out. No trying to pull out just two.
Whoever wired this put these on 20A circuits. They had 12 at the breakers but put #14 on the lights... don't think theres a valid reason for that? One 1900 box where all 3 circuits spliced was overfilled. I removed a union or two and they were not deburred either so I didn't feel comfortable trying to abandon only two of the 3.....
Whoever wired this put these on 20A circuits. They had 12 at the breakers but put #14 on the lights... don't think theres a valid reason for that? One 1900 box where all 3 circuits spliced was overfilled. I removed a union or two and they were not deburred either so I didn't feel comfortable trying to abandon only two of the 3.....
#4
They had 12 at the breakers but put #14 on the lights... don't think theres a valid reason for that?
#5
all three had to come out. No trying to pull out just two.
I removed a union or two and they were not deburred either so I didn't feel comfortable trying to abandon only two of the 3.....
#6
Member
Thread Starter
Join Date: Oct 2013
Posts: 487
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Sure, there was at one time. That used to be allowed by the NEC just like using a 15 amp switch on a 20 amp lighting circuit.
I have a few other circuits where I found #14 on the switch legs and switched the breakers from 20 to 15 because of this....
#7
When was this allowed?