#12 and #14 in same conduit?

Im running a 20A circuit for laundry. 2x12
I like to use the same 1/2" emt to run 2x14 for a 15A lighting circuit.

Is it bad practice to mix the gauges in the same conduit?
 
  #2  
Old 03-03-14, 11:32 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Is the laundry in the same structure as the panel supplying it?
 
  #3  
Old 03-03-14, 11:38 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,974
Received 194 Upvotes on 170 Posts
You can mix conductor sizes in the same conduit. An EGC, if run, needs to be sized for the largest circuit.
 
  #4  
Old 03-03-14, 12:20 PM
bigboypete's Avatar
Banned. Rule And/Or Policy Violation
Thread Starter
Join Date: Dec 2013
Posts: 201
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yes laundry is in basement and lighting circuit is also in basement both supplied from same panel.

Is mixing the two atypical? Would this be considered sloppy work or wouldn't pass the inspection?
 
  #5  
Old 03-03-14, 12:53 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,974
Received 194 Upvotes on 170 Posts
No code issues as long a conduit fill rules are observed.
 
  #6  
Old 03-03-14, 06:46 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,302
Received 868 Upvotes on 731 Posts
Mixing wire sizes is done all the time. You should group the wires of each circuit (hot/neutral, hot/hot, ect.) together with tape at each junction box.
 
 