armored cable
Is flexible metal conduit rated to be grounded?
What fitting is best to connect to metal box?
Do I use bushings?
Intend to use 1/2" flex to junction box for can lights. The flex would be 3ft length?
What fitting is best to connect to metal box?
Do I use bushings?
Intend to use 1/2" flex to junction box for can lights. The flex would be 3ft length?
#2
Is flexible metal conduit rated to be grounded?
What fitting is best to connect to metal box?
Do I use bushings?
What fitting is best to connect to metal box?
Do I use bushings?
https://www.google.com/search?q=flex...w=1024&bih=685
#3
Member
Thread Starter
Join Date: Nov 2013
Posts: 304
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Just to clarify, I have emt/conduit system. So if I branch off one box to a switch box, I have to run a separate ground as well or does the mechanical ground between the boxes and connector suffice?
#4
So if I branch off one box to a switch box, I have to run a separate ground as well or does the mechanical ground between the boxes and connector suffice?
Flexible metal conduit and armored cable are two different things.
#5
Member
Thread Starter
Join Date: Nov 2013
Posts: 304
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Flexible metallic conduit is not rated to be the mechanical circuit ground
Flexible conduit will automatically be grounded when it is connected to the grounded metal box.
#6
So which is it? Do I need to run a ground wire between the two boxes to achieve my mechanical ground?
Flexible metallic conduit is not rated to be the mechanical circuit ground and must have a ground wire pulled through it to the device box.
What material should I use here flexible metal or AC?
#8
Member
Join Date: Oct 2013
Location: United States
Posts: 189
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Fmc
I thought that you could go 6' using FMC as the grounding conductor?
#9
Where flexibility is not required after installation of the FMC, a grounding conductor is not required and...
(5) Listed flexible metal conduit meeting all the following
conditions:
a. The conduit is terminated in listed fittings.
b. The circuit conductors contained in the conduit are
protected by overcurrent devices rated at 20 amperes
or less.
c. The combined length of flexible metal conduit and
flexible metallic tubing and liquidtight flexible metal
conduit in the same ground-fault current path does
not exceed 1.8 m (6 ft).
d. If used to connect equipment where flexibility is necessary
to minimize the transmission of vibration from
equipment or to provide flexibility for equipment that
requires movement after installation, an equipment
grounding conductor shall be installed.
conditions:
a. The conduit is terminated in listed fittings.
b. The circuit conductors contained in the conduit are
protected by overcurrent devices rated at 20 amperes
or less.
c. The combined length of flexible metal conduit and
flexible metallic tubing and liquidtight flexible metal
conduit in the same ground-fault current path does
not exceed 1.8 m (6 ft).
d. If used to connect equipment where flexibility is necessary
to minimize the transmission of vibration from
equipment or to provide flexibility for equipment that
requires movement after installation, an equipment
grounding conductor shall be installed.
#10
I have to say That's a new one on me, I've never seen it done that way. 
I always recommend pulling a separate ground wire and not rely on the conduit ground so I think I'll just keep making that recommendation.

I always recommend pulling a separate ground wire and not rely on the conduit ground so I think I'll just keep making that recommendation.